Originally Posted by gregzoll
Problem with those testers, they do not telll you if there is a "Bootlegged" ground somewhere.
I use an Ideal Suretester for inspections. It shows bootlegged grounds, voltage and current drops, and noise. Also capable of testing two wire systems.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 06-03-2013, 07:54 PM   #47
Rewards Points: 6,652
That is about the only one that I would trust. If the inspector just used one of these http://www.lowes.com/pd_292761-12704...eal&facetInfo= not the kit that you have, I would be calling the AHJ back to get a real inspector in there. All I am taking is the OP word, and assuming that the inspector just used a pocket tester, not the one that you have, by their statement of "little plug in device".
If I could sneak the Suretest by the wife, which I have done with quite a bit of computer network gear of late, it is one that I have been looking at along the lines, to replace two of the test gear that are getting out of dated. Problem is, I only use most of my test equipment about two or three times a year, when I have friends or family call me, stating that they have issues with their places.
I only bought the cheap breaker tester that I did, because of the issue a friend of my wife and mine was having with her place, trying to figure out what outlets fed what breakers. Halfway through the tracing, I was about ready to throw it across the room, because of how cheap the "toy" is.
Old 06-03-2013, 08:08 PM   #48
electures's Avatar
I use the same toy sometimes when I only need to check for correct wiring in a new installation. I use the Ideal when I need to do a thorough inspection.
Old 06-08-2013, 03:25 PM   #49
electures's Avatar
Originally Posted by Philly Master
422.31 Disconnection of Permanently Connected Appliances
422.33 Disconnection of Cord-and-Plug-Connected Appliances.
Funny that the NEC would put the requirements for the cords on Garbage disposals if it was not in the code .....
422.16 Flexible Cords.
None of what you posted "requires" a receptacle. A receptacle is "permitted" however.
The Following User Says Thank You to electures For This Useful Post:
Philly Master (06-08-2013)
Old 06-08-2013, 04:37 PM   #50
Rewards Points: 512
You're a Master, how the heck do you get so much wrong, Philly? None of the above cited articles require a cord and plug!
Installation is the Reverse of Removal.
Old 06-08-2013, 05:21 PM   #51
Electrical Contractor
Philly Master's Avatar
Rewards Points: 516
Where,s the disconnect for the permanently installed appliance ...dishwasher
Philadelphia Master Electrician-Generac Dealer
Philly Master is offline   Reply With Quote
Old 06-08-2013, 06:13 PM   #52
Rewards Points: 512
the branch-circuit switch or circuit breaker
Old 06-08-2013, 09:30 PM   #53
electures's Avatar
422.31(B) States that the breaker can be used as the disco as long as it is within site or has a provision for locking or adding a lock to the breaker.
Old 06-08-2013, 09:34 PM   #54
Gfi vs leapfrogging
I am putting in a wet bar in my basement. I have one 20 Amp circuit ran for my electrical outlets above the counter. I am hoping to keep all of these outlets (9) on the single circuit. I am installing a 20 Amp gfi as the first outlet in this circuit and the remaining 8 recepticles will be after this gfi. My question is as follows..."would installing gfi recepticles in all 9 locations on this circuit serve the same protection against two small appliances simultaneously shorting out the same circuit as would "leapfrogging the recepticles on alternating circuits"?
Won't a gfi recepticle at each location isolate any short in that circuit to the specific recepticles where the short occurs?
I really don't want to run another circuit just for the purpose of being able to leapfrog the recepticles....
whodikai is offline   Reply With Quote
Old 06-08-2013, 10:08 PM   #55
Resi EC
Rewards Points: 252
a wet bar would only require one cicuit, it is not a kitchen. unless it has provisions for cooking, like a range.
GFCI protection is required to all receptacles within 6' of the sink, regardless if they are for the bar or not.
How you do your GFCI protection is up to you
(question for electrians/inspectors) is a circuit for a bar required?
feeling lazy don't want to look it up
Gac66610 is offline   Reply With Quote
The Following User Says Thank You to Gac66610 For This Useful Post:
whodikai (06-08-2013)
Old 06-08-2013, 10:11 PM   #56
Great! Thanks for the help.
Old 06-08-2013, 10:35 PM   #57
electures's Avatar
A separate circuit is not required.
The Following 2 Users Say Thank You to electures For This Useful Post:
Gac66610 (06-09-2013), whodikai (06-08-2013)
Old 06-08-2013, 10:48 PM   #58
Thank you for the response!
Installing rough electrical porch light box RM575 Electrical 9 10-17-2012 03:42 PM