Roof Heat Cables, Dedicated Curcuit ? - Electrical - DIY Chatroom Home Improvement Forum
Old 05-29-2013, 06:55 AM   #1
Lord of Slums
Rewards Points: 1,974
Roof heat cables, dedicated curcuit ?
I am running 100 feet of heating cables on my roof. Can I plug into the outside receptacle. It is a 20 amp circuit. Their are four receptacles on the circuit. Do I need a gfi protected circuit, and does it need to be dedicated. Are their special receptacles used for these heating cables?
mj12 is offline   Reply With Quote
Old 05-29-2013, 07:22 AM   #2
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
You will have to look on the packaging to add up the wattage of the cables. It will usually tell you how many watts/ft.
Old 05-29-2013, 07:41 AM   #3
JW
mm11's Avatar
Rewards Points: 592
You do need GFCI protection for those cables.
mm11 is online now   Reply With Quote
Old 05-29-2013, 09:52 AM   #4
Rewards Points: 1,418
Most install-it-yourself roof heating cables have plugs for standard 120 volt receptacles.
Outdoor receptacles should have ground fault circuit interrupter protection.
You should limit the heating cable wattage to 80% which is 1900 watts for a 20 amp circuit or 1450 watts for a 15 amp circuit.
Old 05-29-2013, 12:09 PM   #5
k_buz's Avatar
Gfi not necessary...there is an exception for snow melting equipment.
The Following User Says Thank You to k_buz For This Useful Post:
Jim Port (05-29-2013)
Old 05-29-2013, 12:58 PM   #6
JW
mm11's Avatar
Rewards Points: 592
I had to look it up myself, because I wasn't sure. 2011 NEC requires ground fault protection of equipment for snow melting equipment (426.28).
The Following 2 Users Say Thank You to mm11 For This Useful Post:
mpoulton (05-29-2013), MTN REMODEL LLC (05-29-2013)
Old 05-29-2013, 04:46 PM   #7
k_buz's Avatar
I am trying to figure out why they would even put that exception in there and the only thing I can come up with is that the plug in variety of gutter cables is not considered fixed. But even then the exception doesn't say you can ignore GFI protection. I apologize...this is 2 times in a week I read too quickly.
Old 05-29-2013, 05:16 PM   #8
Code05's Avatar
Rewards Points: 1,104
GFPE is not the same as GFCI and GFI is not in the NEC.
210.8 Ground-Fault Circuit-Interrupter Protection for
Personnel. Ground-fault circuit-interruption for personnel
shall be provided as required in 210.8(A) through (C). The
ground-fault circuit-interrupter shall be installed in a
readily accessible location.
Informational Note: See 215.9 for ground-fault circuitinterrupter
protection for personnel on feeders.
(A)(3) Outdoors
Exception to (3): Receptacles that are not readily accessible
and are supplied by a branch circuit dedicated to
electric snow-melting, deicing, or pipeline and vessel heating
equipment shall be permitted to be installed in accordance
with 426.28 or 427.22, as applicable.
426.28 Ground-Fault Protection of Equipment. Groundfault
protection of equipment shall be provided for fixed
outdoor electric deicing and snow-melting equipment.
Code05 is offline   Reply With Quote
Old 05-29-2013, 07:32 PM   #9
Semi-Pro Electro-Geek
Rewards Points: 2,852
If the heat cable is plugged into an exterior 120V receptacle, it must be GFCI protected. All exterior 120V receptacles require GFCI protection, regardless of what's supposed to be plugged into them. If it were direct-wired or ran on something other than 120V, then it would be OK to use GFPE instead of GFCI - but GFPE breakers are more expensive and harder to find.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is offline   Reply With Quote
Old 05-29-2013, 07:36 PM   #10
Code05's Avatar
Did you read the exception I posted?
And yes GFPE breakers are nasty expensive.
The Following 2 Users Say Thank You to Code05 For This Useful Post:
frenchelectrican (05-30-2013), mpoulton (05-29-2013)
Old 05-29-2013, 08:51 PM   #11
Ha, nope. I had the page open for a couple hours before I posted my response and didn't refresh it first! I did not realize the melting/GFPE rule provided an exception to the receptacle GFCI requirement. That's interesting.
Old 05-30-2013, 12:48 AM   #12
" Euro " electrician
frenchelectrican's Avatar
Also not many place do carry GFPE breaker at all that useally a special order item and almost all the big box store I know of they don't stock them at all.
Just the common run of mill GFCI.
Readers just beaware that the GFCI and GFPE is not the excat the same beast as you think of.,,
The common GFCI are set at 6ma range.
The GFPE are not common and they are set at 30 ma level which it will not be used for personal protection on North Americian side at all.
Merci,
Marc
Are you ready for SNOW & ICE ? Roofmaster417 Roofing/Siding 15 10-09-2011 10:25 AM
Should I add 2 rotary turbine vents to roof to reduce summer heat? pcumming Roofing/Siding 3 09-30-2011 09:26 AM
Heat Pump will not cut off sunliner HVAC 13 05-17-2011 06:38 AM
Need opinion on this roof profenx Roofing/Siding 14 10-12-2010 01:56 AM
Utilizing heat from Black roof?? Throy Roofing/Siding 2 09-21-2009 04:45 PM