Old 06-03-2010, 06:10 PM   #1
romex cable
is 2/3 romex ok for a 100 amp. sub-panel. also is the ground wire sufficient.
kgh60 is offline   Reply With Quote
Old 06-03-2010, 06:27 PM   #2
Xtreme DIY'r
romex cable
Where are you located ?
How far to the sub panel ?
Old 06-03-2010, 10:33 PM   #3
I=E/R
a7ecorsair's Avatar
romex cable
A sub panel requires the two hots, a neutral, and a ground. Is the sub in the same building as the main or will you be burying the cable underground? Do you already have the cable and if so, what is actually printed on the cable for a wire type? You asked if the ground wire is sufficient but you don't say what size the ground is. 2/3 wire tells me you have three #2 wires and no ground.
a7ecorsair is offline   Reply With Quote
Old 06-04-2010, 03:59 PM   #4
romex cable
is 2/3 romex & its ground sufficient for a 100 amp. sub-panel . the panel is 40 feet away from the main panel. also it is in the same building. from n.y.
Old 06-04-2010, 04:01 PM   #5
Licensed electrician
romex cable
Copper or aluminum?
Old 06-04-2010, 04:03 PM   #6
Master Electrician
romex cable
Cu or AL conductors?
Originally Posted by Jim Port View Post
Copper or aluminum?
Damn I'm slow.
2-2-2-4 Al SER 75amps
1-1-1-3 Al SER 85 amps
1/0-1/0-1/0-2 Al SER 100 amps
brric is offline   Reply With Quote
Old 06-04-2010, 04:11 PM   #7
romex cable
the romex cable 2/3 is copper
Old 06-04-2010, 04:14 PM   #8
Master Electrician
romex cable
95 amps
Old 06-04-2010, 04:17 PM   #9
romex cable
do you know if the 2/3 romex copper not ser cable is ok for 100 amp. sub - panel.
Old 06-04-2010, 04:21 PM   #10
Master Electrician
romex cable
Should be if it is installed in a dry location.
What brand is it?
Old 06-04-2010, 04:23 PM   #11
romex cable
if i us a 90 amp. 2-pole breaker on the 2/3 romex will that be sufficient, for a sub-panel
Old 06-04-2010, 04:28 PM   #12
Master Electrician
romex cable
If your total load doesn't exceed 90 amps.
Old 06-04-2010, 04:29 PM   #13
romex cable
it is in a dry location,i don`t know the brand.
the ground wire in 2/3 romex is a#8 wire.
Old 06-04-2010, 04:36 PM   #14
Master Electrician
romex cable
If it's romex it should be marked on the sheathing.
Old 06-04-2010, 04:42 PM   #15
romex cable
it is a #8 ground wire. is it sufficient for the sub-panel.
Cable question tommy_vercetti Home Theater 15 09-26-2009 10:10 AM
Romex Cable and fibreglass insulation fmva Electrical 4 11-13-2008 01:34 PM
Cut resistance of Romex cable? KE2KB Electrical 3 10-25-2008 03:37 PM
Allowed to run more than one romex cable through a single hole in a joist? J187 Electrical 7 08-17-2007 09:46 AM
Coaxial Cable Question bahaisamurai Home Theater 9 08-08-2007 03:54 PM