-   -   Romex 6/2 NM-B Wire and Conduit (http://www.diychatroom.com/f18/romex-6-2-nm-b-wire-conduit-160559/)
AngelArs 10-19-2012 12:33 PM
I need to run some Romex® 6/2 NM-B wire (around 40 feet) from my garage to my basement. One of the walls it's going through is masonry. Does code require I use conduit? If not, is there any harm in running it through conduit? Thanks :)
rjniles 10-19-2012 01:50 PM
Conduit not required but you can sleeve it thru the masonry.
What will you use the 6/2 for?
AngelArs 10-19-2012 01:56 PM
I am in the process of planning a generator/transfer box install. I know that 6/2 is overkill but one day I may want to upgrade to a bigger generator and don't want to have to rewire. I want to do the wiring once and do it right :)
rjniles 10-19-2012 02:12 PM
Unless you are planning on a 120 volt generator with not plans to ever upgrade to 240, I would run 6/3
Glennsparky 10-19-2012 02:14 PM
You're going to need 6-3 with ground. 6-2 is for 120V generators. 6-3 is for 240V ones. Are you using a transfer switch? Or an interlock kit?
AngelArs 10-19-2012 02:32 PM
I'm sorry, after reviewing you are correct, I'll be running 6/3. Thanks for catching that before I ordered the wire. The inlet box will be a Reliance PR50. Pretty sure the transfer box will be the Reliance Q510C because a Generac transfer box would require a subpanel. So far the generator will be the Generac XG7000E.
joed 10-19-2012 02:34 PM
Garage to basement will need to fire block sealed.
AngelArs 10-19-2012 02:39 PM
Really? Didn't need to do this when I ran the wire for my compressor. What is the best way to fire block seal?
rjniles 10-19-2012 02:44 PM
Fire block caulk
http://www.grainger.com/Grainger/3M-...121019194309:s
Lots of other brands also.
Any building supply, electrical supply or home center carries it
AngelArs 10-19-2012 02:49 PM
OK THANKS! :thumbsup:
I was planning on caulking anyway so I'll just use that kind. I will be using Fire Block insulation also.
rjniles 10-19-2012 03:10 PM
You might want to look at Aluminum SER 4-4-4-6 cable. Will be cheaper than 6/3 NM copper
AngelArs 10-19-2012 04:12 PM
Reliance PR50 instructions specifically state to use only solid copper wire.
k_buz 10-19-2012 05:29 PM
6-3 Romex will not come in solid.
AngelArs 10-19-2012 05:54 PM
Solid as in solid bare copper strands.
mpoulton 10-19-2012 06:03 PM
That's not what "solid" means with respect to wire. "Solid" means one single cylinder of metal per conductor. More than one is "stranded". #6 solid copper does exist (even #4 solid exists), but it's really unpleasant to work with, and you won't find cable that size with solid conductors.