Old 04-04-2008, 12:27 AM   #16
UAW SKILLED TRADES
 
Stubbie's Avatar
 
Join Date: Jan 2007
Location: Kansas
Posts: 5,227
Rewards Points: 2,424
Default

Rigid Nonmetallic PVC Conduit Schedule 40 question?


Quote:
Yes, derating will stop him before he meets the fill requirements.
This would depend on the circuit length after he transitions from the conduit.

If the conduit is 4 feet long but not longer than 10 feet and the cables extend 40 feet from the point of transition (end of the conduit) then I would not have to derate the cables.

Advertisement

Stubbie is online now   Reply With Quote
Old 04-04-2008, 09:13 AM   #17
Cow
Member
 
Join Date: Jan 2008
Location: Oregon
Posts: 116
Rewards Points: 75
Default

Rigid Nonmetallic PVC Conduit Schedule 40 question?


Quote:
Originally Posted by Stubbie View Post
This would depend on the circuit length after he transitions from the conduit.

If the conduit is 4 feet long but not longer than 10 feet and the cables extend 40 feet from the point of transition (end of the conduit) then I would not have to derate the cables.
You are correct, I missed that article.
Cow is offline   Reply With Quote
Old 04-04-2008, 10:17 AM   #18
UAW SKILLED TRADES
 
Stubbie's Avatar
 
Join Date: Jan 2007
Location: Kansas
Posts: 5,227
Rewards Points: 2,424
Default

Rigid Nonmetallic PVC Conduit Schedule 40 question?


I'm very impressed Cow....not many are aware of that. My guess is that you are going to be correct with having to derate the cables though.... also as you know Chris was correct in applying 312.5(C) along with the possibility of using 310.15(A)(2) Exception 2 he may not have to derate.

Advertisement

Stubbie is online now   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Conduit Fill & Ampacity capndave Electrical 37 03-26-2008 03:16 PM
Conduit, above ground, code question davewest Electrical 6 02-27-2008 04:55 PM
Wire size and type in Rigid Metal Conduit Al the Diy guy Electrical 5 02-05-2008 09:31 PM
Rigid insulation question Endeavor General DIY Discussions 2 07-17-2007 11:27 AM
Rigid Metal Straight Threads rjordan392 Electrical 2 06-24-2007 12:42 PM




Top of Page | View New Posts