Are there any sizes available other than 60A, 100A and 200A? Do residences ever have 3ϕ service?
I'm trying to tie in the max. amps with these average usages.
http://www.eia.doe.gov/emeu/consumpt...on_tables.html
Old 04-01-2009, 10:55 PM   #2
Typical load centers here are rated 125 and 200. I occaisionally see a 60 amp 4 space unit.
We do have some 3 phase 120/240 delts services here in the older neighborhoods. The used then strictly for the AC units in the olden days (50's/early 60's)
220/221 is offline   Reply With Quote
Old 04-02-2009, 12:09 AM   #3
Idiot Emeritus
Rewards Points: 1,492
My house has a 120/208 3 phase wye, but it's very rare to see 3 phase to a house. As stated above, I've seen a few 240 deltas with single phase panels and a delta breaker feeding an A/C unit.
I've seen 60, 100, 125, 150, and 200 to a house, but I suspect the 150s are really 200 amp panels with 150 amp mains.
Rob
micromind is offline   Reply With Quote
Old 04-02-2009, 12:49 AM   #4
Rewards Points: 2,350
It seems the vast majority of old fuse boxes I run into are 60 A or 125 A. Old breaker panels are often 100 A. I see 150 A boxes occasionally. And most services installed since the late 70's are 200 A. I have installed 200, 400, 600, 800, and 1200 A services on residences.
But the majority of residential services I come across are 100 or 200 A.
Old 04-02-2009, 09:14 AM   #5
Thanks, folks. . .
Old 04-02-2009, 10:25 AM   #6
31b
sparky
the big McMansion's typically have 3 phase, but it's pretty rare for a conventional residence to have it.
31b is offline   Reply With Quote
Old 04-02-2009, 11:15 AM   #7
31b
sparky
Originally Posted by fast1 View Post
why is it rare for the conventional residence to have it?
you don't need that much power.
Old 04-02-2009, 12:03 PM   #8
Licensed electrician
Rewards Points: 1,054
Three phase seems to be limited to certain areas. No need for it in neighborhoods so the utilities save the money be not having to put it on the poles.
Old 04-02-2009, 12:36 PM   #9
I see 3 phase in some older neighborhoods feeding several houses. The houses services are of course, split phase.
Even a McMansion probably won't need 3 phase. Unless your name happens to be Billy Gates and you bathe in $$$.
rgsgww is offline   Reply With Quote
Old 04-02-2009, 04:03 PM   #10
Rewards Points: 266
Come to think of it, I never seen a house around here have a three phase service, unless the owner has a shop that has three phase, and the house gets fed off that.
There are some apartments in downtown areas that get what they call network service, which is two hots and a neutral, but off of a 208Y/120 4 wire secondary. (hots are any two random legs of the three)
There's even a few houses in town that only have 120 volt service.
junkcollector is offline   Reply With Quote
Old 04-02-2009, 08:50 PM   #11
Idiot Emeritus
The reason so few houses are 3 phase is simply cost.
To supply single phase, the POCO needs two primary lines. Either one hot and the neutral, or two hots. There is one transformer. The secondary (from the transformer to the meter) needs to be 3 conductor.
If the service is 3 phase, a minimum of 3 primary lines are needed. If all 3 lines are hots, the service can be either an open delta, a closed delta, or a wye. The open delta needs two transformers, the closed delta and the wye need 3 transformers. The secondary here is 4 wires.
If the service is a delta, the secondary will have a 'high leg'. There will be 240 volts between any two hots, two of the 3 hots will be 120 volts to neutral, the 3rd hot will be 208 to neutral.
If the service is a wye, there will be 208 (not 240) volts between any two hots, and all 3 hots will be 120 volts to neutral.
I would strongly not recommend installing a 3 phase panel in a house that's fed by a delta system. A 3 phase wye would be fine though. The reason being that sooner or later, someone will install a single pole breaker on the high leg, and send 208 volts to a 120 volt device. With obvious results! A single phase panel with a delta breaker (feeding an A/C unit) is fine. The only place the high leg exists here is the 3 phase A/C unit.
A 3 phase delta panel installed in a commercial/industrial building is OK, usually persons installing breakers in these buildings are more experienced, but I've still seen plenty of stuff blown up by the high leg here as well!
The only reason I can think of to install a 3 phase service to a house is because the house is huge, or there is 3 phase equipment that's not practical to run from a phase converter.
Rob
Old 04-02-2009, 09:49 PM   #12
i've seen a house with a 3 phase delta panel indoors...they stil; had the red tabs on the buss for the stinger leg....this is a disaster waiting to happen, some diyer or handyman is going to come along and hook a circuit up to the stinger
NolaTigaBait is offline   Reply With Quote
Old 04-02-2009, 10:23 PM   #13
Electrician
Rewards Points: 760
Then the Mr Handyman will find out rather quickly why it is called the bastard phase.
darren is offline   Reply With Quote
Old 04-02-2009, 10:29 PM   #14
31b
sparky
natural selection.
Old 04-03-2009, 11:35 AM   #15
Master Electrician
JohnJ0906's Avatar
I've only seen one house with a 3 phase service - 1600 amps.
30,000 sq ft "single family" with a pool and outbuildings.
John from Baltimore
One Day at a Time
"Experience is what you get when you were expecting something else"
"The bitterness of low quality lingers long after the sweetness of low cost is forgotten"
JohnJ0906 is offline   Reply With Quote
framing, expanding wall opening wall - load bearing? nave Remodeling 5 01-23-2008 04:44 PM
Load Calculation ? RM575 HVAC 9 07-04-2007 01:37 PM
% total roof load on interior bearing wall? Grommet Building & Construction 1 03-29-2007 08:37 AM
Automatic load control steel Electrical 3 02-23-2007 06:40 PM
moving another load bearing nailfun Carpentry 2 02-20-2007 09:10 AM