Old 08-04-2011, 01:47 AM   #1
Replacing old hood with over-the-range microwave
So I just bought a nice new over the range microwave and installed it myself with some help.
Everything went relatively smoothly except for when I wired the outlet.
The old hood was hardwired so when I took it down I shut off the breaker, drilled a hole in the cabinet above, and ran the wires up. I figured when I was done installing the microwave, I'd simply mount a box inside the cabinet and hook the wires up to an outlet so that I could plug in the new microwave.
I did all this, plugged the microwave in and went downstairs to turn on the breaker. My wife said that when I flipped it back on, a shower of sparks came from the outlet and the microwave did not turn on. If I run an extension cord to power the microwave elsewhere it works fine. Based on what shut off when I turned off the breaker, this ciruit is shared with one outlet in the kitchen plus (off all things) the washing machine in the basement. Neither of these things was being used at the time, nor did the breaker re-trip. Just sparks and no power.
I'm at a loss. What did I do wrong?
Nathan0115 is offline   Reply With Quote
Old 08-04-2011, 05:44 AM   #2
dSilanskas's Avatar
Take the outlet box apart that you made up. Make sure you don't have the hot touching the sides of the metal box.
dSilanskas is offline   Reply With Quote
The Following User Says Thank You to dSilanskas For This Useful Post:
NJMarine (08-04-2011)
Old 08-04-2011, 07:28 AM   #3
What he said. I suspect hot was touching the box, neutral, or ground and made sparks. It should be obvious when you open the box. Did it trip the breaker??
Old 08-04-2011, 09:37 AM   #4
Well that's the weird part. It did not trip the breaker.
What's more, I only get the spark shower if something is plugged into the outlet I rigged when I turn the power on.
If there was a short circuit in the box, I would be seeing the big pop regardless of what's plugged in there, yes?
Old 08-04-2011, 10:01 AM   #5
seansy59's Avatar
Keep the breaker off for now.
I am Not an electrician
When you have sparks like that, it's not very likely that something is overloaded. That means theres a dead short in contact with metal/ground. When something is overloaded, your breaker will trip which is overcurrent.
First, I take it that your gang box is metal?
Check that there is NO bare wiring or screws touching the box. Bare wire to green screw (Ground), black to brass screw (Hot), white to silver screw(neutral)
- If that still causes a problem, then your outlet may be faulty. Try a new outlet?
- Maybe there is a knick in the wires touching something, that may have
happened when you moved the wire/fan.
seansy59 is offline   Reply With Quote
Old 08-04-2011, 11:44 AM   #6
If I were you, I'd run a separate circuit for the microwave. The way the circuit you tied into is shared, I guarantee the breaker will trip if you try to nuke something while the washer is running.
The Following 2 Users Say Thank You to md2lgyk For This Useful Post:
frenchelectrican (08-05-2011), Speedy Petey (08-04-2011)
Old 08-04-2011, 12:14 PM   #7
Average Joe/ex-Navy IC3
gregzoll's Avatar
Also sharing with the washer is not code compliant.
The Following 2 Users Say Thank You to gregzoll For This Useful Post:
Old 08-04-2011, 12:27 PM   #8
Lic Electrical Inspector
electures's Avatar
- Maybe there is a knick in the wires touching something, that may have happened when you moved the wire/fan.
WHen you take the box apart look for any indication of the short such as blackened areas around the connector or terminals.
All responses based on the 2011 NEC.
If you live in New Jersey click
. All other states click
Please check with local, county and state officials as laws may vary.
Sizing motors
. Online motor calculator
. Online calculators
electures is offline   Reply With Quote
Old 08-04-2011, 12:29 PM   #9
electures's Avatar
Check the manufactures installation instructions and see if they require or recommend a seperate circuit. Now may be the time to install one.
Sizing motors
Old 08-04-2011, 02:53 PM   #10
Licensed Pro
Since an over the range microwave is also a hood, and it is cord and plug connected, then the circuit supplying it should be an individual i.e., dedicated, branch circuit. (see 422.16(4))
The Following 2 Users Say Thank You to HouseHelper For This Useful Post:
gregzoll (08-04-2011), Jim Port (08-04-2011)
Old 08-04-2011, 06:32 PM   #11
Sounds like it may be wired wrong if it only happens with something plugged in. I'm no electrician so I look it up every time. The hot and neutral go on opposite sides of the outlet on a specific side. And the ground has it's own separate green colored screw
Dwillems is offline   Reply With Quote
Old 08-04-2011, 06:41 PM   #12
gregzoll's Avatar
Yes, it is Black to Brass, White to Silver.
Old 08-04-2011, 07:35 PM   #13
electures's Avatar
Try plugging something else in. Maybe there is a short in the appliance.
Sizing motors
Old 08-04-2011, 11:46 PM   #14
Missouri Bound's Avatar
The appliance is (at least it was) fine. You have a hot wire touching to ground. Could be another wire, could be the box. Inspect the box for any blackened areas. Did you use stranded wire, by chance?
Old 08-05-2011, 07:21 AM   #15
Electrical Contractor
Where did the power come from?
If it sparks only when something is plugged in, you could have pulled from a switch leg!
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
range hood opening is bigger than range hood jacks16 HVAC 2 06-23-2011 07:19 AM
OTR Microwave -> Range hood wiring A for Effort Electrical 2 07-31-2010 11:00 AM
Replacing range vent hood goldbedr Appliances 0 04-12-2010 12:27 AM
Installing a range hood NewHandyman Electrical 1 08-10-2009 10:42 AM
Range hood and microwave shelf install??? osueric27 HVAC 2 01-05-2009 01:01 AM