Replacing an exterior electrical panel
I need to replace my panel box. It does not have a main disconnect. It is wired hot, straight from the meter base. Is this unusal or common. The house was built in the 70's. Does the power company have to pull the meter or can I disconnect the power somewhere else
the power company would disconnect the line at the pole, not the meter, generally.
as to unusual or uncommon; No, as long as you have a main breaker in your panel. |
That is what I meant, there is no main disconnect in my electrical box (panel).
There are some older panels with no main disconnect. They usually cut at the street, when you update an electrical panel you replace the meterbase, etc. You will most likely need to get a permit pulled and have an inspection. Are you really up to the job? How experienced are you with electrical? I really recommend having an electrician do this. |
I do not know when a main breaker was first required per code but I cannot remember a time when they weren;t.
In reality, it really doesn;t make any diff as to a main or not in your case because you need the power disconnected before the panel. Power company work there. Quote:
shadetree: you need to check into the legality of you doing this work, to begin with. You also need to really think about this and your abilities as well. A bad install can mean more than no power. Fire and death come to mind. |
Nap, have you every seen a split-bus panel? These were installed in an untold number of houses. And a main is still not required where the number of disconnects in the panel doesn't exceed 6. The split bus worked by having one bus that could accept six double pole breakers. Five of the spaces were used for things like the range, and dryer, water heater etc. And the last was used to feed a second bus that contained the branch breakers. This was a lousy idea then and now, but I have made a fortune replacing them, so I can't complain much:thumbup:! |
Actually I do not see a big problem with split mains per se (other than the 1 situation below). It was the manufacture and their problems that was the real problem. I deal with services that have up to 6 "main" breakers all the time. The only problem I see with it is you have a hot bus (double pole section) all the time. There would be a lack of protection if the bus itself shorted out or the line side feed as it would take out the POCO disconnect rather than a panel main. the other problem is they confuse homeowners that are trying DIY and do not understand how they work. |
I really don't know, but it may have been a preference of the poco. All the ones I replaced in Georgia had a sticker on them that says "Property of Georgia Power Company". Apparently, the poco, at one time, was responsible for providing the entire service including the panel. |
Simply not a smart electrician on those jobs. A disco back by the meter would have been quite reasonable in those situations. |
I assume you install one of the combo meters or other external disconnects than run from that to the panel? Oh and if you do, then the "sub-panel" inside needs the neutral and grounds seperated. Ahh, I see why you are making a fortune on these. Jamie |
up here in northern Indiana and southern Michigan, nodody installs an exterior disco. Just not done that way. We also do not run yardage of SE cable inside either though.
If you run service entrance conductors inside, it should either be in conduit (metal is my pref) or it should be SE style U cable. That way if a nail does hit it, it will short out. Big bang but the alternative can be mush worse. |
| All times are GMT -4. The time now is 02:52 AM. |