Originally Posted by Scuba_Dave View Post
Except that the current installation could violate code & Mfg recommendations
What code would be violated?
hayewe farm is offline   Reply With Quote
Old 04-19-2009, 10:53 PM   #17
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,974
Originally Posted by LeeAmes View Post
The cord and plug are not warm to the touch and it is #14ga cord...
And the installation is less than 3 years old.
It's 10 ft
This installation is riddled with violations and obviously was not inspected. Not that that matters to some folks.
There are MANY special codes with regard to pools.
Some key ones are:
- The cord for a pump motor MUST have an insulated ground of not less than #12.
- The cord must not be longer than THREE feet.
- If the receptacle for the pump is between 5-10 feet from the pool it MUST be of the locking type and be GFI protected.
- NO other receptacles are allowed less than 10' from the pool.
- You MUST have a standard 120v GFI protected receptacle between 10-20 feet from the pool.
Any other pool questions let me know.
Speedy Petey is online now   Reply With Quote
Old 04-19-2009, 10:57 PM   #18
Speedy, Thank you, I have never delt with any pool wiring.
Old 04-19-2009, 10:57 PM   #19
I'll also add, anyone giving advice on the electric requirements for pools should darn well know the codes and what they are talking about. There is just too much at risk!
Sorry, but I feel very strongly about this.
Old 04-20-2009, 12:03 AM   #20
The original cord from the manufacturer is 6 ft long and has '12AW GX3C' written on it, so I guess that means it's 12 gauge? It's not on a timer, and I run it for up to 12 hours in the summer.
I had the pool and pump professionally installed and had an electrician install a GFI receptacle specifically for the pool pump, but the pump came from the manufacturer with a 6 ft cord.
I will get a shorter 14 gauge cable to replace the orginal.
Thanks again to everyone for all your help!
LeeAmes is offline   Reply With Quote
Old 04-20-2009, 03:46 AM   #21
Tool Geek
PaliBob's Avatar
Rewards Points: 2,160
Lee the AWG numbers run where the smaller AWG number has a larger diameter hence a lower resistance. 12 AWG wire has 25% wider diameter than 14 AWG. 12AWG cord is better than 14 AWG
Disclaimer
Disclaimer
& Stay Safe
.....Bob Lavery
Old 04-20-2009, 08:09 AM   #22
The NEC has different requirements for pools, based on whether a pool fits the definition of a permanent pool or a storable pool. The main difference that applies here depends on the depth of water that your pool can hold, as well as the installation of the pool (inground, partially inground, aboveground)
For an on-ground or aboveground pool, up to a maximum of 42" water, a pool is considered a storable pool by definition (680.2 definitions, 2008 NEC). Storable pools are not limited to 3' of cord. (680.7(A))
But if a pool is inground, or partially in the ground, or can hold water to a depth over 42", it is a permanently installed pool by definition and is subject to the 3' cord length rule.
I know what I'm going to say is splitting hairs, but I tend to consider a typical aboveground pool as partially in the ground due to the slight excavation and placing of the sand base under the bottom.
If you agree, then it is partially in the ground, and therefore considered a permanent pool. If you don't agree, then it is an aboveground pool, and as long as the pool cannot hold over 42" of water, then it is a storable pool and the 3' cord length is not applicable.
This might be why the mfg had a 6' cord on the pump.
As Speedy and Palibob pointed out, you need a minimum 12AWG flexible cord. The reason is like Speedy said, you need a minimum size 12AWG ground conductor, and a 14AWG cord will not have it. 12AWG is the next size up from 14AWG.
Willis
williswires is offline   Reply With Quote
Old 04-20-2009, 01:37 PM   #23
Good point Willis. I didn't consider this could be one of those "Intek" storable pools.
Old 04-20-2009, 01:45 PM   #24
My Inspector spent more time looking at the pool wiring & the sub I installed then anything else. The pool has been there 30+ years but he wanted to make sure everything met current code - as did I
I had to add one outlet in the pool area to meet the 10-20' rule
There were outlets in the pool cabana, the only other one was on the outside of the pool cabana but was outside of the fenced in pool area
I'm also replacing/moving the outside pool area light
It's halogen & the glass is missing
I'm installing a CFL floodlight instead
in ground pool chad2423 Building & Construction 4 09-28-2009 09:41 AM
Pool Pump Wiring mpdive Electrical 17 06-15-2008 07:30 PM
pool pump BillyD Plumbing 4 05-12-2008 10:07 PM
need instructions on replacing a Whirlpool refrigerator power cord please. ChrisC30 Electrical 2 03-10-2008 09:59 PM
Just to confirm, no GFCI needed for hard wired pool pump..right?? Al the Diy guy Electrical 6 02-10-2008 12:28 PM