Old 07-14-2012, 06:17 PM   #1
replacing a 60 A double slot breaker with 2 30s
I am getting rid of my elec stove replacing it with gas and would like to use the double slot for the basement apartment countertop range and water heater, each 30A, I believe. But the problem is that i am out of slots in my panel and this will free up only two adjacent slots. 30A breakers also require a double slot. I was wondering if there is a solution, like those single breakers that support two circuits.
See attached. The 60A circuit is on top.
replacing a 60 A double slot breaker with 2 30s-forumrunner_20120714_181635.jpg
Old 07-14-2012, 06:24 PM   #2
MarginallyQualified
That's fine. Remove the WIRES which are fed by that breaker.
...countertop range and water heater
Yeah. Use that 60A breaker to feed a small subpanel.
I'd put any/all tenant circuits in there that can be accommodated...
and keep the upstairs & general use stuff (water heater?) in the first panel.
Old 07-14-2012, 06:37 PM   #3
oh but that's more work than i want to do right now. i will eventually split the house in two meters and will do it then.
Old 07-14-2012, 07:10 PM   #4
MarginallyQualified
I'm reminded of a quote...
Never put off till tomorrow what you can do the day after tomorrow-Mark Twain
Oops! Lets try this one:
Never put off till tomorrow that which you can do today. -Benjamin Franklin
Old 07-14-2012, 07:29 PM   #5
thank you for your wisdom, sir, i am in a time crunch, i may go bankrupt if i try to do everything the perfect way rather than focus on wrapping the project up.
so a subpanel is out of question at this time.
thanks
Old 07-14-2012, 09:00 PM   #6
Licensed Electrician
k_buz's Avatar
1) Is your panel rated from tandem breakers? (post a picture of the sticker on the inside door of your panel)
2) Is there a detailed list of what is on each circuit? You could possibly double up some lighter circuits.
3) Gas water heater.
Location...Location...Location
Old 07-15-2012, 08:10 AM   #7
A 240 volt water heater and a 240 volt countertop stove still need double wide breakers. Other circuits would have to be moved to single wide double breakers. You might find a double wide quad tandem breaker with handles 1 and 4 tied together for one 240 volt circuit and handles 2 and 3 tied together for another 240 volt circuit.
In addition to the requirement that the panel and the specific breaker be compatible, each panel has a limit to the number of breaker handles where a double breaker counts as two handles.
The disadvantages of crab apple trees. In summer, the apples are too sour to pick and eat. In winter the birds come and leave dropping all over the place.
AllanJ is online now   Reply With Quote
Old 07-15-2012, 02:55 PM   #8
Semi-Pro Electro-Geek
If your panel accepts them, you could use a 30/30 quad breaker. But a subpanel sounds like the best solution. It's hardly any more work and only a little bit more money.
mpoulton is offline   Reply With Quote
Old 07-15-2012, 03:01 PM   #9
Code05's Avatar
I think that panel is a SQ-D QO, I am doubtful the OP will find a quad 30/30, but maybe.
Code05 is offline   Reply With Quote
Old 07-15-2012, 04:16 PM   #10
The only quad breaker currently manufactured for a QO panel is a 20303020, where the 20's are untied, so you are correct that OP is out of luck.
LooseSCruz is offline   Reply With Quote
Old 07-15-2012, 04:53 PM   #11
The quickest and cheapest way is to take out four 20amp single-pole breakers, install two twin 20/20amp breakers in their place, and attach the four circuit wires to these two twin breakers. Now you will have created two free breaker spaces. Now, take out the 60amp breaker. This will leave you with four open spaces. You can now install the two new 30amp 2-pole breakers for the water heater and stove top.
kontoose is offline   Reply With Quote
The Following User Says Thank You to kontoose For This Useful Post:
amakarevic (07-15-2012)
Old 07-15-2012, 07:12 PM   #12
Electrical Contractor
Without the panel info, we do not know if this panel will accept tandom breakers.
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
jbfan is online now   Reply With Quote
The Following 2 Users Say Thank You to jbfan For This Useful Post:
Code05 (07-15-2012), stickboy1375 (07-15-2012)
Old 07-15-2012, 09:57 PM   #13
Here is the tag. Thanks.
Class CTL-- Panelboard Series L8
replacing a 60 A double slot breaker with 2 30s-forumrunner_20120715_215644.jpg
Old 07-15-2012, 10:44 PM   #14
k_buz's Avatar
No not that tag. The sticker on the inside of the panel door.
Old 07-15-2012, 11:03 PM   #15
Square "D" Q.O. panels, together with their breakers, have no rejection pins that would prevent twin single-pole breakers from being installed. You learn something every day - right...!...
Replacing QOU Air Handler Breaker, help please... Ralph III HVAC 2 03-14-2012 01:39 AM
replacing a breaker lgburke Electrical 1 09-26-2010 11:36 PM
Replacing a breaker Daggerhart Electrical 19 03-15-2010 12:38 PM
Wierd Double Pole Breaker Occurance rlemar Electrical 5 02-16-2010 10:43 PM
single vs. double breaker Neil_K Electrical 3 11-15-2004 12:02 AM