First off, I read thru quite a few messages on this board, and I am REALLY
impressed by the knowledge and helpfulness. By far, this seems to be the
BEST board out there for information, which reflects directly back on the
members!
OK - now for my dilemma.
I currently have an older 200AMP meter panel with 24 breaker slots and the
following circuits.
Slot Name Amp
1 Bath Fans 15
I need to move my meter panel in order to complete a patio remodel.
The plan is to relocate the panel to the new location and install a large
junction box on the interior wall of the house, opposite of the existing
panel. Then run new home runs from the new panel to the junction box and
splice into the existing home runs.
The problem I have is that I cannot locate a 200 amp exterior panel with
enough circuits - the largest 200 amp panel I can find is a 20 slot panel with 40 circuits. (CH MBE2040B200BTS)
I currently have 36 circuits and need capacity for the patio BBQ and lights (20A), patio refer and disposal (20A), landscape lighting (15A), spa (50A)
Doing the math, I come up 1 circuit short.
What I was contemplating doing is mounting an additional sub panel, next to
the new main panel, then installing a 100A breaker in the new panel to feed
the sub-panel (the sub panel has 12 slots for 24 double breakers).
My plan was to punch a pair 2" holes in the sides of both panels (one near
thetop and one near the bottom) and run the sub-feed wires thru the top
holes and run the home-runs from the sub-panel back into the main panel and
then into the conduit already in place at the bottom of the main panel.
I'm assuming that if I use waterproof conduit between the two panels that I
will meet code. My question is, which circuits should I keep in the main
panel and which circuits should I feed from the sub-panel? Or can I even do
this?
I live in the great state of California, Sacramento County to be exact.
It's key that I be able to knock out 2" holes in the side of each box, as I have limited space on top of the new meter and I don't want to route conduit out of the bottom of the new panel either.
this is NOT a subject that any size of reply would be sufficient
Since you do not state your level of skill aqnd experience in this trade
I must assume a couple of things . . .and perhaps yuo will find this useful
* you have NOT done your math . . .please consult an electrician to get
an actual amount of load ...both existing and proposed before you do
anything . . . .you are assuming that you will NOT need , in fact larger
service delivered to handle the total load
* please let me suggest that you have an professional do this . .this is
NOT DIY level work . .get a permit..get inspections
* have the inspector come out . .FIRST . .DISCUSS what you have in
mind . .how he wants to stage the inspections
thanks king - I am not a newbie DIY person. I am an ASE Certified Master Auto Tech with over 30 years experience, I have done 99% of my own home remodels in the past, including replacing a meter panel, additions, flooring, plumbing, etc (only paid for stucco work, because I wanted it to match).
I have a permit and plans. The goof at the permit counter reviewed the plans and approved them. The original plan was to use a Ranch Panel at the side of the house (with a meter) , then run #2ODD wire from the meter to a new breaker box. The inspector said the plan to put the breaker box in a closet did not pass code and told me to take it out. He also said the guy at the counter should not have approved the plans - my loss. Anyone interested in 75' of 2ODD wire and a brand new ranch panel?
He did give me permission to gut the breaker box and use it as a JBOX as long as I screwed the door closed.
I am NOT increasing the the existing load - I'm guessing (and will confirm) that the spares are not really spares and I'm guessing there are a few extra home runs in the wall and in the panel that are unused (previous home owner had some electrical work done).
Sacramento county had to reduce their staff by 12 inspectors. I can't get an inspector to answer a phone or return a call, much less come out to the house. They have been here twice already and threatened to charge me $175 for more trips out to the house.
I had two bids to replace the panel and to bury the service line - $6500 and $5700. I am into this job for a little over $1500, which includes 3 panels, wire, conduit, breakers, trencher rental.
I am capable of doing the work and making the calculations and want to do this right. I'm not trying to cut corners or get "past inspections". I just don't know what is expected and when the plan check guy that approves your plans is not on the same page as the inspector, I get a little pissed off, but you cannot upset those guys, otherwise they will critique every little item.
Again - I will check the spares tonight and report.
Leonard, Please don't take this any way other than constructive critisism.
This is pretty common on this website. People will be planning a kitchen remodel, or adding a hot tub, or in your case a new patio (which i'm sure isn't going to be cheap) but they NEVER factor in the final cost for an issue like this. They have no problem spending 8k on a new hot tub, but get pissed when they have to spend another 2k on electrical work to make it proper and want to DIY it to save some money. Messing with a panel change or move is not for a DIY'er as kingsmurf stated.
I am a fairly advanced DIY'er (by no means pro) and this is something that I would absolutly not undertake alone... possibly under direct supervision of someone who IS a pro.
Hey Andy - no offense taken. AS an auto mechanic, I see it all the time. People get in over their head, because some guy at a parts counter sells you a $37 head gasket kit, you think you can do it.
I am by no means an expert and I don't know the code by heart, but I have done this before and I do 99% of my own home projects. Being a mechanic, I have a natural aptitude for fixing things. Had it been $2500, I would have wrote the check in a heartbeat. I have an electrician coming out tomorrow to take a look at things and either offer some advice or wrap it up for me.
The reason you can't find a panel with more breakers is because the code limits the maximum breakers in a panel to 40. Until your region moves to the 2008 code you are stuck. If you need more circuits then you need a sub panel.
In your list I see 2 spares. You can use the spares for 120 volt or 240 circuit. If you need 240 volts you can move breakers to get 2 open spots for a 2 pole breaker. With two spares listed, why upgrade now? You have enough space for a good bit of power. You can use as many breakers suitable/allowable for your panel to the limit.
If you need more than two slots, why not just install a sub panel near your patio. Then you can have all the circuits you need. Then contact this forum for safely installing the sub panel.
Ps....The spare slots will be used for the sub panel feeders.
There are two spare slots in the box and there are three 14/3 hunks of romex that are in the panel, but are not used. It would appear as though I am going to be OK as is. I should have one extra breaker, but I still need to facilitate a spa breaker, so in essence, I am still short a few slots.
The Home Depots in AZ have 40 space Seimans, Cutlar Hammer and Homeline all in one panel/meter combos.
The issue you will run into is derating your conductors if you run them in a single conduit from the new location to the old one. If there is attic/crawl space, we would run romex from the new panel to the jbox at the old location.
If not, you have to limit the number of current carrying conductors in (depending on local interpetation) or up size them according to some table somewhere.
The only conduit I have is a 2 2" x 3' sections coming out of the bottom of the new panel, then into an LB and then a short (10" piece) thru the wall and then the wires are all under the house for about 20', then they go thru a 3" hole in the sill plate and then up the wall to the new j-box.
The countsy said I could bundle them to gether in the conduit as long as I kept the length of conduit less than 10', which I did.
again...I never mean any inference that a poster does or does NOT have experience . .I can only make genral assumptions based on the original posts
that being said
* it seemed that you were adding a SPA / bbq/ lighting loads etc
. . did I misunderstand / are those already on site and powered up?
* just curious . . .when I am requested to add load to an existing
rather full service . . .I really do a dilligent load test . . .reading the
panel mains . . .or breaker hots if I cant get clamp on feeders . . .
and have the home owner really power the place up . .and note how
close that is to about 70% of max service available . . . then pondering
which appliances/ circuits are going to have an inrush number . .I
make some recommendations
* I was curious if you have done this . .if so what did you obtain
for readings ?
for readings ?
No prob, really. I REALLY appreciate someone taking the time to think things thru, especially when the advice is good and FREE!!!!
I have a fluke meter with an inductive amp probe that will give me a decent reading. So are you saying I should turn everything in the house on, then check the amps thru each main feed?
I do not have the patio installed yet. Another reason for moving the panel is that it is smack dab in the middle of the wall where I plan on hanging a flat screen and the feed line would have to drape over the patio cover - something that is a no-no in my book, plus it won't pass code..
The patio will have:
1 ceiling fan, without a light fixture
4-6 60 way lights
Either rope lighting or some tiki lanterns
TV, DVD and small surround sound amp/receiver
plugs on BBQ island for rotisserie and blender
Garbage disposal in island sink
small refer
I see it taking:
20 A circuit for lighting and fan
20 A circuit for blender, refer, rotisserie and disposal
20 A circuit for TV, AMP and extra plugs
I might end up installing an exhaust fan (range hood) for the BBQ, but I'm not certain just yet.
That leaves me needing 1 20A circuit for a plug at the rear of the property for low voltage lighting (60' from panel to outlet)
and a spa circuit (I'm guessing that's a 50 amp circuit).
Skip the sub panel and use a full 40 space panel. $130 bucks.
In my area they ALWAYS allow the romex to be sleeved outside......but it is against code. NEC considers inside the conduit to be a "wet location" if it's outside and romex isn't reated for wet locations.
Double check with them first.
Be sure and leave a couple inches of sheath on the romex into the panel.
I think you can do it. A good mechanic is a good mechanic. In your case, you will be able to complete a lot of the work ahead of time since you are relocating the service.
Keep in mind that your ufer or ground rods will have to connect to the new meter/panel along with your water and gas bond.
Leonard...Roger..I see that you are good to go mechanically
* I still stress the NUMERO UNO item to be taken care of is
knowing what actual load you are really using before adding anymore
* adding a 240v 50amp per leg inrush load...WILL affect the current load
* this is the one simple step that saves a bunch of grief later . .I have
seen too too many times . . . .additions to the panel/load . . .just like
this..add Lo & Behold when we have sucessfully completed all of the
mechanical aspects of the work . . .we dropped the ball on the very
first electrical requirement
and then the breaker / breakers start tripping
and then a larger service is required and we tear out
quite a bit of what was mechanically swell but electrically
insufficient
do this first before you do anything else . .so you'll know
where you are at ELECTRICALLY . .if after powering up the house
IE lights TV's washer / dryewr/ AV must be running . .AND read
amperage on the inrushes
if you are anywheres near ...say 70% of the dervice connected to
your home and you are not CURRENTLY popping breakers
you must make an electrically sound decision / with all new loads
and inrushes factored in before plunging ahead
I wont bother you with the Call I got from wealthy fella
with gorgeous home on the Golf course . . large wonderful home . .
actually had the inground pool installed.....the spa...the BBQ...some fairly
elaborate exterior lighting . .had the GC I work with at times . .build
all of this . . . . . . .stationed the pool and pump equipment . .over 70
feet away from the pool/spa . .massive inrush to start pushing that
water
then called me to hook it all up to the main panel
needless to say..after I told him what would have to
transpire ( need and much larger service ) I had to
scrap him off of the ceiling.
he did not have me do the work . . .he had someone
the GC knew patch it into the existing panel
I got a call from the GC..wondering what I could do
about the main breaker tripping incessantly . .I relayed the
above paragraph to him
pool/spa/BBQ...party lighting is now non-functional
awaiting the new and much larger service
Leonard..you have a meter..seriously load the house
and obtain those readings,,you'll be happy you did
If you have breakers tripping due to in-rush current, you have more problems than meet the eye.