czak01 01-07-2011 02:37 PM
I need to replace a Bryant Type BRD BR 15-15 CU-AL SWD circuit breaker that failed but I don't think they make them anymore. Is there any other breaker could I buy to replace it, or do I need to try to find a used one? Thanks
brric 01-07-2011 03:00 PM
I believe Cutler-Hammer BD 15-15 is a listed replacement.
PaliBob 01-07-2011 03:40 PM
Take the failed breaker down to an electrical supply house, not to a Home Depot or any other Big Box store. Find an Electrical Supplier in your area. If you are in a really remote location and the nearest supplier is more than an hour away then get a replacement breaker through a local Electrician.
LyonsElecSupply 01-09-2011 10:40 PM
Bryant is now replaced with Cutler Hammer products. A cutler hammer/eaton reseller would be more than happy to take care of you.
And if memory serves me right you can get a BR1515 non CTL breaker. It will fit right in there. :)
It would run you about 10-20 bucks.
blank457 09-23-2012 04:46 PM
I need to replace a breaker Bryant Type BRD BR 15-15 CU-AL and it doesn't have the SWD on it anywhere that I can see. Would the BR1515 non CTL breaker fit mine as well?
corvaxmuzzy 08-12-2014 08:20 PM
This is an old post, but I feel that it could use more info for DIY understanding...
BD vs. BR is going to vary based on notched vs. unnotched bus stabs. The rejection tab is going to limit the application to notched bus stabs only.
Know thy bus stab.
http://i60.tinypic.com/34pkrie.jpg