Removing The Bonding Screw - Electrical - DIY Chatroom Home Improvement Forum
Old 02-03-2012, 12:10 AM   #1
Removing the bonding screw
I've just installed a small sub panel that contains only 1 - 15 Amp GFI breaker for our new hot tub. The panel is next to my main panel. Do I remove the neutral bonding screw ? I am thinking "yes". Or will that effect the operation of the GFI breaker which has the load side neutral connected to the breaker.
Sammy 2 is offline   Reply With Quote
Old 02-03-2012, 12:22 AM   #2
Electrical Contractor
rrolleston's Avatar
Rewards Points: 1,012
Send a message via AIM to rrolleston Send a message via Yahoo to rrolleston
It should have four wires if 240v sub panel and the bonding screw should be removed.
rrolleston is offline   Reply With Quote
Old 02-03-2012, 12:33 AM   #3
retired elect/hvac/plumb
plummen's Avatar
Location: south east of omaha/The island of misfit contractors
Rewards Points: 2,020
If it has a bonding screw are the neutral and ground busses also connected together?
"facts" have no relevance to this discusion
Posting from a concrete bunker under a non descript barn
plummen is offline   Reply With Quote
Old 02-03-2012, 12:40 AM   #4
Plummen, is that not what the screw does, bond the neutral to the frame ? As an afterthought this little panel has room for an additional breaker ( unused ). I am going to check the catalogue number on line, maybe it is considered to be more of a means for disconnect and it is not really considered a subpanel ? At this time it is fed with 12/2 from a 20 amp single pole breaker in the main panel into the 15 amp GFI and out with 12/2 to the tub. ( Could have been 14/2 to the tub which is 120 V / 8.9 amp draw ) There is a neutral bar in the subpanel with a removable bonding screw and also there is a ground screw (s) bolted to the cabinet.
Old 02-03-2012, 12:43 AM   #5
plummen's Avatar
I mean the jumper between the 2 seperate buss bars,the bonding screw normally goes through it to bond both buss bars to the case.
Do you have a picture of inside your panel?
Old 02-03-2012, 12:58 AM   #6
rrolleston's Avatar
Why would you have used this panel if you had room in your panel for another breaker?
Old 02-03-2012, 01:23 AM   #7
Rewards Points: 6,652
Let's start from the beginning. Does this hot tub only require Single phase 240? If so, it should not have a sub-panel, but a pull-disconnect, such as used with a a/c, or a gfci breaker, and a outlet, that the cord from the hottub is attached to, that plugs into said protected outlet. That means, if it does not require two hots, or a combo of 120/240, then it should only have three wires.
If it requires 120/240, then yes, it should have four wires, and as such, it should be wired accordingly.
Old 02-03-2012, 07:42 AM   #8
jbfan's Avatar
Rewards Points: 138
As long as you have seperate bars for the neutral and dround wires, remove the screw.
Old 02-03-2012, 08:00 AM   #9
Rewards Points: 1,418
Disconnect or remove the bonding bar, if any, running between the ground bus bar and the neutral bus bar from the neutral bar.
Remove the bonding screw, if any, in the neutral bus bar.
The ground bus bar needs to be bonded to the panel, by being fastened to the panel back with metal to metal contact, or by having a bonding screw of its own that is digging into the panel back, or with a bracket or jumper wire attached to the panel back.
The Following User Says Thank You to AllanJ For This Useful Post:
plummen (02-03-2012)
Old 02-03-2012, 09:31 AM   #10
Thanks everyone, I have it figured out now.
Do screw heads really need to be mudded with three coats? KUIPORNG Remodeling 33 09-17-2011 02:54 AM
Drywall screw gun or screw setter bit ? Arky217 Building & Construction 6 06-18-2011 10:22 PM
Swapping old 3ways with new (different screw color configuration on new switch) Michblaze02 Electrical 10 11-08-2009 03:17 PM
Would you staple, nail or screw? Speedball Flooring 7 11-28-2008 12:21 PM
Which bonding method proper??? Nestor Electrical 2 09-15-2006 07:18 AM