Old 12-02-2008, 09:10 PM   #1
Recessed light wire size
Hi all -
I am installing recessed can lights. The box nor material states what size wire each light has.... basically I want to run 2 lights off of each junction box in parallel. So the junction box feeds power to the first can light, and that light feeds to the next light. Is there a common wire size provided on these lights? The brand is "Quantus".
Thanks!
jizzle is offline   Reply With Quote
Old 12-02-2008, 09:37 PM   #2
The lighting ciruit will determine what size wire you will use. If the circuit is protected by a 15A breaker you can use 12 or 14 gauge wire. If is protected by a 20A breaker you must use 12 guage wire. Where are you located?
jerryh3 is offline   Reply With Quote
Old 12-03-2008, 08:17 AM   #3
I am referring to the lights - they have a pigtail that you wire to. If a second like is connecting to the first light, at the pigtail, I want to make sure I don't exceed the amperage of the pigtail. The lights themselves don't state what size wire the pigtail is.
I am running 12/2, but the pigtail may be ...?
Old 12-03-2008, 08:31 AM   #4
The pigtail size really doesn't matter since only the current from that fixture will be running through it.
Old 12-03-2008, 08:49 AM   #5
So even though 12/2, light pigtail #1 and light pigtail #2 are all in the same wire nuts, pigtail size doesn't matter? Sorry, just making sure. I've always wired each light to a junction box and am trying to save boxes and wire by doing it this way.
Old 12-03-2008, 08:56 AM   #6
When you are referring to the "pigtail", do you mean the wire that is already in the light junction box?
Old 12-03-2008, 10:56 AM   #7
Moderator
Termite's Avatar
The pigtail/whip wires that come in each fixture are sized for that fixture, and downstream fixtures are not a consideration because the pigtail isn't physically carrying any more current than it's own fixture takes. As long as your branch circuit wiring between the lights is sized correctly for the breaker, you're good.
wire feed size for dble oven setup ? ? ? yes.itsconcrete Electrical 29 09-12-2008 10:11 PM
Wire hot with light switch turned off dangerouswithtools Electrical 3 06-17-2008 08:56 AM
Circuit breakers and wire size stan 41943 Electrical 19 03-06-2008 03:29 PM
Wire size for distance Question fburke Electrical 4 07-28-2007 10:29 AM
recessed lighting wiring to 3way switch DIY4EVER Electrical 1 07-12-2007 02:35 PM