Receptacle Rating Question - Electrical - DIY Chatroom Home Improvement Forum
Old 12-18-2008, 05:19 PM   #1
Rewards Points: 820
Receptacle Rating question
Hi;
I am reading the 2005 NEC, and found this interesting:
210.21 Outlet Devices. Outlet devices shall have an ampere
rating that is not less than the load to be served and
shall comply with 210.21(A) and (B).
Then, subpart (3), and table 210.21(B)(3)
(3) Receptacle Ratings. Where connected to a branch circuit
supplying two or more receptacles or outlets, receptacle
ratings shall conform to the values listed in Table
210.21(B)(3), or where larger than 50 amperes, the receptacle
rating shall not be less than the branch-circuit rating.
Table 210.21(B)(3) Receptacle Ratings for Various Size
Circuit..... Receptacle
Rating..... Rating
Amps...... Amps
15....... Not over 15
20...... 15 or 20
30...... 30
40...... 40 or 50
50...... 50
(sorry about the look of the table. It would not copy correctly from the .pdf, so I typed it in by hand, and the forum editor would not allow me to pad the columns with spaces)
So, if I read this correctly, a 20A receptacle cannot be used on a 15A branch.
This makes no sense to me, since there is really no difference between a 15A and a 20A receptacle; at least not in the ability of each to carry at least the 15A load.
Anyone care to comment on this?
Ultrarunner2017 is offline   Reply With Quote
Old 12-18-2008, 05:24 PM   #2
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
But you may have an appliance that requires a 20 amp circuit, say cord and plug connected that pulls 16 amps. It would have a 20 amp plug that can only be plugged in a 20 amp device. If that device is on a 15 amp circuit, we got problems.
wirenut1110 is offline   Reply With Quote
Old 12-18-2008, 05:26 PM   #3
Take a look at a 15 and a 20 amp receptacle and you'll see a difference. The 20 amp has a "tee" slotted neutral.
hoistdoctor is offline   Reply With Quote
Old 12-18-2008, 06:00 PM   #4
Rewards Points: 820
Oh, OK. I apologize. I have been purchasing only the 20A ones, used on 20A branch circuits, and I hadn't noticed the difference.
I'll have to check, and change if necessary; the receptacle in my closet that is on a 15A branch. I use it for my LAN router.
Hmmm. that brings up another, but unrelated thought: Am I permitted to have a receptacle for any reason in a closet that holds clothing?
Old 12-18-2008, 06:20 PM   #5
Rewards Points: 2,350
Absolutely.
Old 12-18-2008, 06:36 PM   #6
Rewards Points: 820
Originally Posted by InPhase277 View Post
Absolutely.
Thanks. It's a great place for the router.
Receptacle Rating question Ultrarunner2017 Electrical 19 12-20-2008 07:20 PM
15 or 20 amp socket with #10? Mdbuilder Electrical 16 12-11-2008 01:27 PM
Receptacle Wiring Question mpinchinat Electrical 11 12-23-2007 03:02 PM
Split Receptacle on 3-Way Circuit NPS Electrical 6 11-03-2005 10:28 AM
Electrical receptacle replacement question sherlock Electrical 7 05-20-2005 04:33 PM