Old 05-07-2011, 07:17 PM   #1
Receptacle with 50 volts
I lost power in two receptacles. I replaced them, but still have no power, however, my voltmeter shows 50 volts. I can't locate any other receptacles or switches that are not working, and all breakers are on. Any thoughts on possible causes/remedies are appreciated.
neamb2 is offline   Reply With Quote
Old 05-07-2011, 07:36 PM   #2
Electrician
The problem will be in one of the outlets that is working. Sounds like you may have a bad neutral somewhere. You will have to open each box to see if you can find the problem. Try to think how they would have wired it and follow it back.
darren is offline   Reply With Quote
Old 05-07-2011, 07:54 PM   #3
Licensed Electrical Cont.
Speedy Petey's Avatar
Completely agree.
Just a note to future readers with this problem. 99% of the time the problem is NOT a "bad" receptacle. It is a connection.
Replacing a non-working receptacle is good only in that you get a new tighter receptacles, it almost never fixes the problem.
Old 05-07-2011, 07:58 PM   #4
Wire Chewer
Red Squirrel's Avatar
Try plugging an incadescent bulb (lamp, socket etc) in there to see if it lights up. If not, it may be phantom voltage (I'm not that familiar with the cause of it, but it's... interesting lol) or somewhere something is misswired and it's in serries with something else. Could also be a bad neutral as mentioned if it's a MWBC or branched off of one.
Old 05-10-2011, 12:30 AM   #5
Thanks darren. I located the circuit, which has 8 receptacles and 3 switches on it. All work except the 2 mentioned. I'm learning, so...are you saying then I need to open the remaining good receptacles and look for a loose or disconnected white neutral?
Thanks...
Old 05-10-2011, 12:45 AM   #6
Mad Scientist
If you can figure out the path that the circuit follows, the problem is likely in the next outlet upstream, towards the breaker panel, from the outlets that aren't working.
If any of your outlets are wired using the push-in "backstab" holes on the back of the outlets, that could be the source of the problem. You should re-wire them with the wires looped around the side screw terminals for a better, longer-lasting connection.
McSteve is offline   Reply With Quote
Old 06-14-2012, 11:14 AM   #7
I solved the exact same problem two days ago in my basement wiring project. It was indeed a loose neutral in the wiring nut on the receptacle one upstream from the one reading 50 volts. Wish I had read this thread before
InProgress is offline   Reply With Quote
Replacing receptacle with GFCI wiring problem braden Electrical 8 04-06-2011 09:32 AM
low voltage reading at receptacle 2 ball cane Electrical 5 04-06-2011 01:07 AM
Switched Receptacle Question MrBill_DIY Electrical 3 11-21-2010 11:07 PM
New 240V receptacle reads zero volts Madroaster Electrical 32 09-19-2009 01:35 PM
Wiring A Ceiling Fan, Receptacle, and Outside Light merlin6984 Electrical 9 03-26-2009 10:52 PM