Re-routing Wires - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 12-04-2012, 10:52 AM   #16
Special User
Rewards Points: 1,230
Originally Posted by Rochsolid View Post
I agree with electures on this. I usually run 2 cables per 3/4" hole. That's the norm where I'm from, inspectors will fail it if we don't. Also a 1 1/4" hole in your 2x10 joist is a very big hole, I would be worried about the structural strength now of those joists
As a general rule, you can make large holes within the middle 1/3rd of a joist. It's notching or making holes in the top or bottom 1/3 that rapidly destroy the load bearing capacity of a joist.
The above post is for entertainment purposes only. Its contents may, and probably will, lead to legal liability and damage or loss of property, life, or limb. Use at your own risk.
tylernt is offline   Reply With Quote
Old 12-04-2012, 04:55 PM   #17
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
FRom the 2011 NEC;
334.80 Ampacity.
The ampacity of Types NM, NMC, and
NMS cable shall be determined in accordance with 310.15.
The allowable ampacity shall not exceed that of a 60C
(140F) rated conductor. The 90C (194F) rating shall be
permitted to be used for ampacity adjustment and correction
calculations, provided the final derated ampacity does not exceed
that of a 60C (140F) rated conductor. The ampacity of
Types NM, NMC, and NMS cable installed in cable tray shall
be determined in accordance with 392.80(A).
Where more than two NM cables containing two or
more current-carrying conductors are installed, without
maintaining spacing between the cables, through the same
opening in wood framing that is to be sealed with thermal
insulation, caulk, or sealing foam, the allowable ampacity
of each conductor shall be adjusted in accordance with
Table 310.15(B)(3)(a) and the provisions of 310.15(A)(2),
Exception, shall not apply.
more current-carrying conductors are installed in contact
with thermal insulation without maintaining spacing between
cables, the allowable ampacity of each conductor
shall be adjusted in accordance with Table 310.15(B)(3)(a).
As long as the holes are not sealed, or the cable is not in contact with thermal insulation, no derating is required.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Can you use wire nuts on a fan light switch with silvery looking wires? amodoko Electrical 4 10-28-2012 08:26 PM
Are Dead wires allowed or unsafe? Scooby333 Electrical 31 10-01-2012 01:26 PM
240v conduit with different gauge wires... Biospot Electrical 7 12-14-2010 07:07 PM
Removing wall with wires in it jboswald Electrical 11 11-29-2009 02:55 PM
Three hot wires coming into a receptacle? Jeff DIY Electrical 10 10-07-2009 01:35 PM