12-03-2012, 03:47 PM
#1
re-routing wires
We have a lowered ceiling in the kitchen and I am currently raising it. By doing so, I am having to re-route some of the wiring. I have drilled 1 1/4 in. holes through some of the rafters and fed 5 wires through the whole. My question is if this is ok. I was told by someone before that there was a limit as to how many wires could run through a conduit, but was unsure if 5 wires bunched next to each other in this fashion was exceptable.
12-03-2012, 04:53 PM
#2
Lic Electrical Inspector
re-routing wires
If you bundle more than (2) 14/2 romex for more than 24" it will have to be derated. Five cables will have to be derated. What are the gauges of each cable? I am more concerned about the 1 1/4" hole through the rafters. You may have weakened the rafter.
All responses based on the 2011 NEC.
If you live in New Jersey click To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . All other states click To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. .
Please check with local, county and state officials as laws may vary.
Sizing motors To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . Online motor calculator To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . Online calculators To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. .
The Following User Says Thank You to electures For This Useful Post:
12-03-2012, 05:09 PM
#3
re-routing wires
12-2 wire. Actually it was 2x12 floor joists for upstairs. How would you re-route wire? How many wires can be bundled for how many feet?
12-03-2012, 05:13 PM
#4
E2 Electrician
re-routing wires
IMO, running wires through bored holes is not bundling, the joist are typically 1.5" thick, thus does not meet the 24" length requirement to be considered bundled, you can run as many wires as you wish in bored holes, the only time this is an issue is when fire stopping is required, then you run into the max. 9 current carrying conductor rule, and are limited to that or derating must take effect.
The Following User Says Thank You to stickboy1375 For This Useful Post:
12-03-2012, 05:21 PM
#5
re-routing wires
What would be the problem with the wires being bundled anyway? Of course we have to describe "bundled" Five 12-2's running through several 2x12's for approx. 14 ft. would be ok then?
12-03-2012, 05:23 PM
#6
E2 Electrician
re-routing wires
The problem with bundling, when cables and wires are actually bundled, is heat dissipation...
And I don't see an issue at all with what you propose.
12-03-2012, 05:25 PM
#7
E2 Electrician
re-routing wires
And two NM's are already derated, its only an issue when we get to 9 current carrying conductors.
12-03-2012, 05:33 PM
#8
re-routing wires
So the heat issue is really dealing with the "length" in which the wires are "enclosed"? (Cannot be enclosed for more than 24") The wires touching one another wouldn't be an isssue? Hey. I'm a truck driver, not an electrician! HA HA
12-03-2012, 05:34 PM
#9
re-routing wires
I agree with electures on this. I usually run 2 cables per 3/4" hole. That's the norm where I'm from, inspectors will fail it if we don't. Also a 1 1/4" hole in your 2x10 joist is a very big hole, I would be worried about the structural strength now of those joists
The Following User Says Thank You to Rochsolid For This Useful Post:
12-03-2012, 05:35 PM
#10
E2 Electrician
re-routing wires
They can touch, you're fine with what you did....
#11
E2 Electrician
re-routing wires
Then the inspectors are morons... so which code section did they fail you on?
EDIT
Eh. you're canadian... that changes things.
12-03-2012, 06:03 PM
#12
re-routing wires
EDIT
I've never heard of anyone running that many wires thru one hole.
12-03-2012, 06:07 PM
#13
E2 Electrician
re-routing wires
It's a non issue.... I dont see any code violation.
12-03-2012, 11:57 PM
#14
re-routing wires
As far as derating is concerned, I wouldn't be concerned with it. But as you add cables to a hole, you build up more friction as you pull each additional cable through. I've seen the outer shell of romex worn away and all the way through the THW insulation as well (yeah, I'm an old electrician). So I always limit myself to two.
Adding more holes in the joist (within reason) won't hurt anything.But do yourself a favor, drill every other joist as you drill your holes, and at the end, turn around and go back and drill the joists that you skipped. This will make pulling the romex through your holes much easier.
And I always unroll my roll of romex on the floor and never pull it directly from the center. This will add a twist that will act as a "rasp" that can damage existing cables in a given hole.
The Following 2 Users Say Thank You to rootboy For This Useful Post:
12-04-2012, 10:23 AM
#15
Thread killer
re-routing wires
EDIT
Unless its a manitoba thing, in Ontario, we can run it the way you propose. Has to be bundled for more than 2 feet here, as well. Running it through joists doesn't count as bundling. (I'm not 100% sure, but I think we have to start derating at 7 conductors though.)
You can have it good, fast or cheap. Pick two.
The Following 2 Users Say Thank You to Canucker For This Useful Post:
| Thread Tools |
Search this Thread |
| Display Modes |
Linear Mode