I need some assistance with a bonding jumper wire at my house. To give some background:
I live in California in a house that's about 80 feet long, and the circuit breaker box (100 amps) is in the back of the house. At the front of the house is where my water comes in (all copper plumbing). The people that lived in this house before either hired a lazy electrician or lazy plumber to install the bonding jumper wire. This person installed this long 80 foot run along the top of my roof's fascia boards, causing all kinds of leaks due to the nailing of the conduit. It's also very difficult on the eyes with the conduit running all along the house.
I want to re-route the bonding jumper underneath my house in the crawlspace, but am not sure what kind of wire to buy. I've read a bunch of references to #8 bare copper soft drawn -- is that right? If so, is there a recommended place to buy it? The big box stores sell 250'+ for $200 and the local electrical store wants $1 a foot because I don't have an account with them. I only need 100' at the most.
t60 is offline   Reply With Quote
Old 07-30-2012, 12:50 PM   #2
Licensed electrician
The size of the GEC is determined by the size of your service. What size is your service?
This is not a bonding conductor, but the grounding electrode conductor.
Old 07-30-2012, 12:57 PM   #3
t60
My breaker box is 100 amps. There is a grounding rod in front of the circuit box already connected to the breaker using #8 bare copper.
Old 07-30-2012, 01:05 PM   #4
t60
And you're right, it's a GEC required by my city..
Edit: I think I found the answer from my city website
Copper: solid, stranded, bare or insulated
#8 can be used, but requires EMT/armor cable or conduit
#6 can be used and requires protection only if subject to physical damage
#4 can be used and only requires protection if subject to severe physical damage
Old 07-30-2012, 02:14 PM   #5
Master Electrician
If there's already a grounding rod at the panel why does he need to jump on the water pipe too?
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
Old 07-30-2012, 02:30 PM   #6
t60
It's required by my city. There are three methods of GEC, and the water jump is required. I then have to utilize one of the two remaining methods, either a grounding rod or a ground to my slab.
Old 07-30-2012, 02:42 PM   #7
The NEC requires a water line ground to be supplemented with another electrode.
The Following 2 Users Say Thank You to Jim Port For This Useful Post:
andrew79 (07-30-2012), t60 (07-30-2012)
Old 07-30-2012, 02:47 PM   #8
t60
Now that that's answered, does anyone know if I can run two grounding wires in the same conduit pipe? The #8 solid copper for the grounding rod, and a future #6 insulated wire for the plumbing?
My circuit breaker is encased in stucco, and this would save me a ton of time. Otherwise I will have to chip away at the stucco wall a bit and run some conduit through it.
Old 07-30-2012, 03:34 PM   #9
Electrical Contractor
Can you pull the exsisting wire and reuse it to save you money?
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
Old 07-30-2012, 03:51 PM   #10
t60
I could, but honestly it won't be worth the work for me. The replacement wire will be ~$80 and the existing run is high up and pretty stiff. I may end up recycling the wire, but I don't plan on re-using it as it'll be tough to get it down in one piece.
Still wondering about using two wires in one conduit pipe..
Old 07-30-2012, 03:57 PM   #11
No issues as long as the pipe is sized for the two conductors.
If the pipe is metallic you will need a bond bushing at the ends.
t60 (07-30-2012)
Old 07-30-2012, 04:00 PM   #12
t60
Awesome, there's one there on both ends for the grounding rod and in the service panel. Looks like I'm good to go. Thanks so much for the info!
Old 07-30-2012, 04:00 PM   #13
Master Electrician
Another question. Does the nec require conduit fill taken into account for grounds? Here we don't have to. We are also not allowed to pull bare ground into emt.
Old 07-30-2012, 04:05 PM   #14
The NEC does allow bare grounding conductors in a conduit.
The conductors do count towards cross-sectional fill.
convert 3 wire range junction box to receptacle filby Electrical 0 06-05-2011 02:33 AM
Carrier Infinity 69 Trouble Code 42 bodya1 HVAC 4 12-05-2010 07:43 PM
Adding ground in old home ChaosTheory Electrical 6 06-16-2010 05:02 PM
Low Voltage Wire Shorting Rdakota06 Electrical 3 07-22-2009 02:15 PM
Ground rod or not? brotherman Electrical 30 07-15-2008 05:58 PM