#1 |
re: NM3 60 degree cable inquiry.
Hello,
I have NM3 60 degree celcius/ 140 degree farenheight cable in my walls. I had planned to install insulation in my house where no insulation currently exists. In the past, if these wires heated up, the cavity is large enough that the heat could potentially dissipate relatively quickly. However, if i insulate the walls, i insulate the wire, and it is the potential of overheating past the 60 degree rating. What are some possible solutions to this problem besides rewireing everything? Is there such thing as a 13A cicuit breaker to be installed my circuit breaker panel? (limiting the current, would decrease the maxiumum temperature.) would this actually work? thanks Last edited by gramps416; 12-12-2011 at 12:29 PM. |
#2 |
Electrical Contractor
Thats 140 degrees, so if you are overheating the wires, you need to find that problem and fix it.
That wire has been installed in insulation for years.
Yes I am a Pirate, 200 years too late. "Jimmy Buffett" |
#3 | |
re: NM3 60 degree cable inquiry.Quote:
My extra usage and introduction of insulation is a concern. Last edited by gramps416; 12-12-2011 at 12:35 PM. |
#4 |
No need to worry all. NM cable is commonly has a 60 degree rating. Houses very rarely have 75 or 90 degree conductors unless they are installed in pipe. Which is usually overkill anyway!
#5 |
Licensed Pro
NM-B type cable contains 90C conductors. This is the Romex type cable currently installed in most homes over the last few decades.
"Life is hard. Life is harder when you're stupid." John Wayne |
#6 |
you can insulate without problem, 60C cable have 15 amp ampacity for 14 ga wire, the 90C one has the same rating
#7 | |
To licensed electricians: I want to know, according to the NEC, does this statement still hold true today in 2011? Last edited by gramps416; 12-12-2011 at 06:01 PM. |
#8 |
Don't have the article in front of me but it is stated that NM cable, even rated at 90 degrees celsius, shall be derated from the 60 degree C in the ampacity table.
#9 | |
Electrician
From the 2011 NEC: 334.80 Ampacity. The ampacity of Types NM, NMC, and NMS cable shall be determined in accordance with 310.15. The allowable ampacity shall not exceed that of a 60°C (140°F) rated conductor. The 90°C (194°F) rating shall be permitted to be used for ampacity adjustment and correction calculations, provided the final derated ampacity does not exceed that of a 60°C (140°F) rated conductor. The ampacity of Types NM, NMC, and NMS cable installed in cable tray shall be determined in accordance with 392.80(A). Where more than two NM cables containing two or more current-carrying conductors are installed, without maintaining spacing between the cables, through the same opening in wood framing that is to be sealed with thermal insulation, caulk, or sealing foam, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(3)(a) and the provisions of 310.15(A)(2), Exception, shall not apply. Where more than two NM cables containing two or more current-carrying conductors are installed in contact with thermal insulation without maintaining spacing between cables, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(3)(a).
Kyle Just because you can, doesn't always mean you should |
#10 |
Thanks SD. It's much easier when you actual have the article handy.
#11 |
i have tried my best to understand what the limits of the 60 degree cable is. Can someone explain this to the laymen?
-g |
#12 | |
The limit is that a #14 wire is rated at 20 amps, but code allows a max of a 15 amp breaker. If your wires are getting close to 60 degrees, you have other problems. That is layman terms. Insulate the walls and don't worry about the wire.
#13 |
I didn't realize that the cable had more capacity than 15A, since that is code. That is what what I found confusing that NEC said 20A.
So you are right, I don't have anything to worry about. -cory |
| Display Modes | |
| Need help sizing Generator cable | dgajr | Electrical | 2 | 07-20-2010 01:07 AM |
| Evaluating a kinked cable | dave11 | Electrical | 5 | 05-09-2010 11:20 AM |
| broken drum snake cable, how to fix? | confusedDIY | Plumbing | 1 | 03-18-2010 09:38 AM |
| Underground service entrance cable requirements. | kgt55 | Electrical | 9 | 06-22-2009 07:55 AM |
| Running Sky+ cable | bookersbeauty | Electrical | 1 | 04-09-2009 08:12 PM |