Random GFI Tripping - Electrical - DIY Chatroom Home Improvement Forum
Old 11-23-2010, 03:42 PM   #1
Random GFI tripping
I have a GFI circuit breaker in my main panel for both bathroom outlets that trips randomly. It will reset but trips hours and sometimes days later. There seems to be no problems when everything is on and pluged in. Two blow dryers, curling iron, at the same time and doesn't trip. Should we replace the GFI?
amyfspence is offline   Reply With Quote
Old 11-23-2010, 03:59 PM   #2
DIY'er
jamiedolan's Avatar
Rewards Points: 1,024
You could try replacing it and see what happens. It could be a bad breaker and false trips. Also could be something that is really causing a fault and it isn't in error. Are you sure the outlets / fixtures are all securely installed and there are no moisture / water issues?
Jamie
Jamie Dolan - Neenah, WI
Jamie Dolan Paw Dogs
Need Help Uploading Photos? Click here.
jamiedolan is offline   Reply With Quote
Old 11-23-2010, 06:33 PM   #3
" Euro " electrician
frenchelectrican's Avatar
Just before you plan to replace the RCD { GFCI } Breaker check the receptales for any moisture or anything out of normal format.
And make sure the ground { Bare } is not touching the netural otherwise it will trip the RCD pretty fast.
Most single pole RCD breakers typically run about 30 or so Euros.
Merci.
Marc
Old 11-24-2010, 03:48 AM   #4
Rewards Points: 1,192
I would suggest replacing the gfci breaker with a regular one,and use gfi devices where necessary. No feed through.
bobelectric is offline   Reply With Quote
Old 11-24-2010, 05:32 AM   #5
Tool Geek
PaliBob's Avatar
Rewards Points: 2,160
Amy, Welcome to the Forum
I agree with bobelectric on replacing the breaker with two GFCI receptacles.
Disclaimer
& Stay Safe
.....Bob Lavery
Old 11-24-2010, 07:26 PM   #6
At the moment I'm having a similar problem with a T8 flourescent fixture, with an electronic ballast. It has a pull chain switch and is plugged into a GFCI receptacle.
At random intervals when its shut off with the switch, it trips the GFCI.
I have plugged and unplugged this fixture and it never trips the GFCI. However, whenever I use the switch to shut it off, it causes a trip.
The switch is a single pole switch that opens the hot conductor only.
It my hunch that a collapsing magnetic field from the ballast is generating current in the neutral which causes the GFCI to trip.
I would suggest that any device that has a motor or transformer that has a collapsing magnetic field and a single pole control switch can very likely cause GFCI's to trip.
Old 11-25-2010, 12:58 PM   #7
Tool Geek
PaliBob's Avatar
Originally Posted by Wildie View Post
...... I would suggest that any device that has a motor or transformer that has a collapsing magnetic field and a single pole control switch can very likely cause GFCI's to trip.
I have a related situation where a GFCI breaker feeds a ceiling fan (continually set to High speed) that is controlled by a wall switch fan speed control that has a slider switch that goes from Off, low,med, high.
If I rapidly switch from Off to med or high, the GFCI breaker always trips. If I go from Off to low, then wait for the fan to come up to speed, then switch to med, the GFCI breaker does not trip.
There are other lights and a few outlets on the same circuit but it is only the fan speed control that has ever caused a trip.
I built a GFCI margin tester to help find leakage problems but had no luck finding a problem with the fan speed control.
GFCI Tester
Disclaimer
& Stay Safe
.....Bob Lavery
Old 11-25-2010, 02:45 PM   #8
Electrical Contractor
kbsparky's Avatar
If you have a surge-protected power strip in one of those bathrooms, replacing the GFI devices will not solve this issue.
Surge-protector power strips can shunt power surges to ground, thus creating an event that the GFI senses as a ground fault. This will occur at random times, regardless of whether you are using anything plugged into it or not.
-KB
Old 11-25-2010, 03:33 PM   #9
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,192
Would using a double pole switch (normally for 240 volt application) solve this problem? Interrupt the hot and neutral at the same time. Assuming you have the hot/neutral in the switch box and not just a switch loop.
Coastal South Carolina
Old 11-25-2010, 04:07 PM   #10
Yes! i think that this would do the trick! This Chinese fixture cost me $18 and a pull chain DPST switch would probably cost this much again.
The OP's problem is that bathroom appliances are causing trips, and it wouldn't be practical to change a hair drier over to a DPST switch.
I posted my problem, so as to point out that its not likely that its a GFCI fault, its a bug with the use of various devices on GFCI circuits.
Especially, the questionable stuff thats coming from China, these days.
Old 11-26-2010, 10:18 AM   #11
Electrical Supplier
Rewards Points: 150
I would replace the breaker with a standard and GFCI outlet everything that needs to be.
Did anyone else notice this: "Two blow dryers, curling iron, at the same time and doesn't trip. Should we replace the GFI? "
I would IMMEDIATELY replace that breaker. It is NOT functioning correctly as an OCPD. Those 3 loads combined are in the neighborhood of 4000 watts or 33 amps........
As far as the t8 fixture goes, Tripping a GFCI could be expected when switching. Fluorescents rely on the grounded reflector to create the magnetic field. Ballasts must be grounded. 5mA current leak is all it takes to trip most GFCIs. Its just a bad combination of ballast brand and GFCI brand. Thats all.
Id say remove the GFCI and hard wire it in to remove the problem. (As hard wired fixtures dont require GFCIs)
LyonsElecSupply is offline   Reply With Quote
Old 11-26-2010, 02:22 PM   #12
The flourescent fixture is temporarily being used in the laundry area. The code in my area requires this GFCI receptacle.
I'm just on the verge of completing a reno. project and the lighting will be on its own circuit, when its finished.
GFCI keeps tripping on and off at random times helter Electrical 2 07-27-2010 08:32 AM
Problem with random tripping. Timb7 Electrical 12 04-30-2010 09:15 AM
Dead Breaker? and Nusiance Tripping... jasonblu Electrical 9 11-06-2009 06:13 PM
Random GFCI tripping, Data Rack theatretch85 Electrical 5 07-10-2009 08:20 PM
Tripping Wrong Breaker woodworksnmore@comcast.ne Electrical 15 03-28-2008 01:47 PM