Questions Regarding 100amp Service And Panel Upgrade - Electrical - Page 3 - DIY Chatroom Home Improvement Forum
Old 12-12-2012, 08:57 AM   #31
Rewards Points: 27
Originally Posted by k_buz View Post
Is that price for a real service upgrade, or a panel change? I'm guessing the latter.
Panel change, replacing aluminum wires with copper, and add new breakers. I got it down to $800 including a 100 amp 30 spaces Siemens panel plus a whole house surge Siemens protector. I asked the electrician, would this stop the lights from flickering...this was his response:
"If the lights are flicking that means the line is overloaded.
Your panel has aluminium service wire so this can be a issue also for flicking light
New panel will have copper wires up to roof
If I will replace service wire (copper) this should stop flicking"
asledge is offline   Reply With Quote
Old 12-12-2012, 09:28 AM   #32
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
When do the lights flicker?
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 12-12-2012, 10:16 AM   #33
Rewards Points: 27
When the dishwasher changes cycles, or when the fridge starts cooling cycle, all the lights flicker.
Old 12-12-2012, 10:37 AM   #34
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Just to add to the mix in my juristiction the utility does not run 150 amp service your choices are 100 to 200 amp that's it .. same with the meter. Of course you can go bigger but that is not relevant here.
So what I'm saying is the utility if they must change the meter and utility drop or lateral from.. for example .. an existing 60 amp service ( these are very old services ) your choices would be 100 or 200 amps or 400 amps brought to your house. 100 amps is the NEC minimum at todays standards. If you chooose 200 amps you can hang any panel you want equal to or less than that service size down to 100 amps.
Point here is that you need a load calc done or your inspecting juristiction will not sign off on a service upgrade. It normally is a required item to get the green tag. The other point is your contractor (he should know this) can't just hang a 150 amp panel with 150 amp main breaker on a 100 amp service. I think the others have been saying the same thing just trying to add some clarity.
Old 12-12-2012, 02:41 PM   #35
Since when does the fact its aluminum service wire effect a dishwasher or lights? Copper and aluminum carry similar current, assuming the corresponding gauge wire is used.
I bet the feed to the dishwasher is shared with all sorts of other stuff also, not the service wire being a different element. There is a reason fridges are now supposed to be on their own circuit. My kitchen was wired so that the fridge, several lights and an outlet were all on the same run... not anymore!
OmegaWS6 is offline   Reply With Quote
Old 12-12-2012, 04:14 PM   #36
Rewards Points: 27
Ok, so I basically need to tell him when he upgrades the panel, to make sure to put the fridge, dishwasher, and lights on 3 separate circuits. Is there a particular size breaker for each? Since it's a 100 amp 30 space panel, I'm guessing there should be sufficient capacity on the panel to split up stuff. I am also adding around 20 can lights in the house, which I am hoping will be on a separate circuit as well.
Old 12-12-2012, 04:22 PM   #37
Electrical Contractor
jbfan's Avatar
Rewards Points: 420
I'd say that is a very cheap price to replace the panel, and the exsiting service with copper.
jbfan is online now   Reply With Quote
The Following 2 Users Say Thank You to jbfan For This Useful Post:
asledge (12-12-2012)
Old 12-12-2012, 06:14 PM   #38
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Is he pulling a permit? Is he licensed? Is he replacing the meter socket?
The price seems way too low. You know what they say about being too good to be true?
Old 12-12-2012, 11:57 PM   #39
" Euro " electrician
frenchelectrican's Avatar
I just got a quote from an electrician to update the Zinsco panel to a 100amp Seimens panel from home depot:
This is his estimate:
Service Upgrade 100 Amp
Installation of new 100 Amp Siemens panel 30 spaces
Pass the electrical pipes to the new panel
Installation of new breakers
Price include all material and labor
Siemens 100 Amp 30-Space 30-Circuit Indoor Main Breaker Load Center
Model # P3030B1100CU Internet # 203027295 Store SKU # 593867
He is charging me $1000 even. The panel only costs $87. Do you think I could find someone else who will do it for cheaper than that? Does this too much just to update the panel?
1,000 USD ? well IMO it is on the low side but the key issue is how easy do that electrician can route new cable or conductors in conduit plus what more they will have to sink in two new ground rods as well if not mention in there. ( for USA side )
If you going to have the Electrician replace the service by upgrading expect the power outage up to 8 hours if they can get the inspector to come by before the day is " over " they can put a approved sticker on and the same time many POCO will only reengerized it up only after the inspector say ok.
So be prepeared for that if you have anything that is cricital you may want to ask the electrician to bring the genertour or other power source to keep your fridge cold or whatever it needed to be.
Make sure that Electrician do get the permits line up before they can do anything with it.
Merci,
Marc
100amp service to 200amp service - double or single panel CapeCod153 Electrical 8 05-09-2012 08:03 PM
Questions about 100-200A service upgrade kwilcox Electrical 35 04-22-2012 05:15 PM
Main Service Panel to 2 breaker panels - I can imagine you all rolling your eyes kalus Electrical 22 03-23-2012 02:09 AM
Upgrade from 100amp to 200 amp service: What can stay? jimmyfloyd Electrical 11 01-09-2012 06:04 PM
Wiring Size Calculations for New Service CorinthWest Electrical 7 12-07-2010 11:36 AM