#1 |
Questions about subpanel in a new shed
I just recently put down a deposit on another shed. I'm planning on installing a subpanel there for electric heat & light for housing small birds (nothing heavy like welders or power tools). I've installed my own branch circuit within the house successfully for a gas hot water heater with a power vent as well as other various small electrical projects around my house, so I'm familiar with the basics. I'm a computer hardware engineer by trade.
I understand I need to use conduit for this type of thing, and I have a few questions about the conductors, breakers, and the conduit:
Greg |
#2 |
No. Don't route the conduit that way. Go up and to the left. This way you only have one 90 degree bend. You are only allowed 360 degrees for a run of conduit before you need a pull box (Jbox). You have plenty room to go up and over. You don't have to go up all the way. Just put a small outward kick in the conduit to bring your 90 flush with the studs. Then you can strap it to the studs. No plywood required.
Also, the exposed NM cables shown above should be sleeved. The NEC prohibits NM cables to be in a position where the can be damaged. Note: Use the search function above. Its loaded with information on sub panels. Loads of information. Any question you have is answered if you look for it. Last edited by J. V.; 03-17-2011 at 11:45 AM. |
#3 |
J.V.,
Thanks for your response. I had hoped there would be a less convoluted way of starting this run from the panel, but I wasn't sure if I was allowed by code to make a turn like that from the side of the panel to the adjacent stud. I think I'll use a flexible elbow to route it from the panel to a point on the side of the stud and go from there unless you or anybody else knows of a reason why this shouldn't be done. About the NM cable above - do you mean all of it that was shown in the picture or just the two sections coming up that stud and heading off to the left where I'm planning to run the conduit? Is there a way I can sleeve it without having to rip it all down and re-do it? Thanks for the tip - I have searched these forums and found lots of good information such as the 360 degree rule you mentioned, subpanel information, and the maximum number of conductors allowed in conduit. I just wanted to be sure I interpreted it all correctly. Thanks again, Greg |
#4 |
Scared Electrician
recommend 1" pvc conduit-easier to pull wire.
Ragged Trousered Philanthropist Please follow the code - its there for your safety no matter how inconvenient. |
#5 | |
Questions about subpanel in a new shedQuote:
The cable situation was mentioned, because its a violation to install NM cable where subject to physical damage. By no means do you have to do anything as "subject to physical damage" could mean anything, but you get the picture and so does the NEC. However. Since it looks like a mess, why not clean it up and sleeve the cables up close to the ceiling. Any cables that run perpendicular to the studs should be pulled through holes drilled in the studs or behind the studs. They should also be in holes at the top sill. Installed as if you planned to put up drywall for an example. Do you understand? Just turn off the breaker for the cable. Disconnect the cable from the panel, pull it out, insert a sleeve and reinstall. You will need some conduit, some connectors with lock nuts and some plastic bushings. You want a connector at the top of the sleeve with a bushing. PVC can be used. I like EMT, but it will be harder for you to work with. The picture on the top is just for general cable routing and the picture on the bottom is showing a sleeve with connector and bushing at the top (yellow). Sorry I could not find something matching your application, but these pictures should make this more clear. I hope? Don't tell anyone, but you could just ignore the cables. I promise not to tell.
#6 |
Scared Electrician
why not just install a piece of plywood and now they are protected?
#7 |
And squash the cables between the plywood and the studs? Those cables need to be in the stud (through bored holes) or behind the studs to install any plywood or wall board of any type.
| Tags |
conduit, subpanel ![]() |
| Display Modes | |
| Adding a subpanel to a sub-panel and other questions | CardinalPilot | Electrical | 14 | 03-30-2011 03:23 PM |
| Adding Subpanel for Basement - Few Questions | mindle | Electrical | 28 | 01-07-2010 09:49 AM |
| Shed questions | Piedmont | Electrical | 12 | 10-20-2009 10:06 PM |
| A few slightly different questions on subpanel wiring. | Chris Dopp | Electrical | 8 | 06-26-2009 10:45 PM |
| Subpanel to Shed - Check my plan | NateHanson | Electrical | 9 | 04-26-2007 10:56 PM |