Question Regarding Bonding Screw. - Electrical - DIY Chatroom Home Improvement Forum
Old 10-08-2013, 03:14 PM   #1
Question regarding bonding screw.
I had an electrician over to the house today to hook up my house panel (2) to my garage panel (3) and move power from box (4) to box (2) as it is a new panel. He told me that there didn't need to be a bonding screw in panel (2).
Here is how everything is laid out.
Power from the pole comes to a box on the outside of my house box (1) there is a disconnect on that box and grounding rods connected to it.
From (1) is used to go to (4) but I had a new panel (2) put in and while redoing existing electrical I will run everything to the new panel (2). I had the electrician move the line from (1) - (4) to now be (1)-(2) and a jumper from (2)-(4) to power existing things in (4).
From (2) to garage (3) everything is connected correctly as supplied by other posts on this forum. (3) has its own grounding rods and the bonding screw is removed.
I asked is box (2) needed a bonding screw and he said because box (1) has a disconnect and is grounded (2) didn't need the bonding screw. I cannot see anywhere in the old old box (4) where a bonding screw would go but the box is so old I wouldn't even know if one is there or not.
So with all that said just to double check does box 2 need a bonding screw in the box or no?
P.S. Box 1 and box 2 are about 15 ft from each other. (box 2 and 4 are 2 feet apart)
Thanks,
dabeast is offline   Reply With Quote
Old 10-08-2013, 03:18 PM   #2
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
No bonding screw, it's bonded in box #1.
Can you take a pic of box #2 to see if there's a strap or screw in there that needs to be removed?
wirenut1110 is offline   Reply With Quote
Old 10-08-2013, 04:03 PM   #3
Licensed electrician
Rewards Points: 1,608
The bond screw or strap is only installed if they are service panels. Any panel downstream of the first means of disconnect do not get the bond screw or strap installed.
stickboy1375 (10-10-2013)
Old 10-08-2013, 04:23 PM   #4
Master Electrician
Rewards Points: 3,866
Originally Posted by Jim Port View Post
The panels are only bonded if they are service panels. Any panel downstream of the first means of disconnect do not get bonded.
Just a bit of semantics here, Jim. The panels(tubs) get bonded. The downstream neutrals do not get bonded.
brric is online now   Reply With Quote
Old 10-08-2013, 04:59 PM   #5
I reworded my response for clarity. Thanks,
Old 10-08-2013, 05:43 PM   #6
He removed the green bonding screw that was there when he said it wasn't needed.
I did the same in the box in the garage on advise from users here in another post. I just didn't do it in box 2 because I thought it was the main panel for the house.
Old 10-08-2013, 05:45 PM   #7
And I only needed to put grounding rods at my garage because of the distance from the panel in the house correct?
Old 10-08-2013, 05:47 PM   #8
A grounding electrode is needed at detached structures regardless of the distance from the service panel when the building is served by more than one circuit.
dabeast (10-08-2013)
Old 10-08-2013, 05:50 PM   #9
Ok thanks. I feel confident in my setup now and I can start installing lights in my garage.
I'm just glad I didn't attempt to actually hook everything up. I did all the hard work of pulling the lines and installing the boxes just not hooking it up.
Old 10-08-2013, 07:09 PM   #10
joed's Avatar
Rewards Points: 12,852
The feed between the panels must be a four wire to carry the ground from the initial bond at panel 1 to all the others.
Old 10-09-2013, 08:28 AM   #11
Rewards Points: 510
Great! I was just curious because some older panels had neutral bars that you can't "unbond" from the can so, it required installing insulated neutral bars.
Old 10-09-2013, 09:12 AM   #12
they still make them and are labeled 'suitable for use as service equipment only'. you can't use these for sub panels (without 'modification', of course).
itsnotrequired is offline   Reply With Quote
Old 10-09-2013, 09:17 AM   #13
Rewards Points: 510
Seems I've been running into them more and more doing generator installs
Along with the "house ropers" putting the main breaker on top for a bottom fed panel
Old 10-09-2013, 09:25 AM   #14
Hahaha the electrician actually switched my box around cause it is bottom feed and I had the main breaker on top (Box 2). With the feed to the garage going out the top, I must say the box looks way cleaner than having 2 big loops in there.
The Following User Says Thank You to dabeast For This Useful Post:
wirenut1110 (10-09-2013)
Old 10-09-2013, 09:26 AM   #15
Each leg of feeds is 4 wire. I made sure of this on suggestions by other threads here.
Missing bonding screw in panel justinae Electrical 20 04-10-2013 04:47 PM
Help! Glowing spot at bonding screw WillK Electrical 85 12-16-2011 08:22 AM
Can't get set screw in TP holder loose janralix Plumbing 4 08-12-2009 10:47 PM
Question about removing a screw type fuse box... OmegaBunny Electrical 9 09-15-2008 10:13 PM
Bonding & Ground Rod Question bradsguns Electrical 3 06-13-2008 12:55 PM
