Question On GFCI With Shared Neutral - Electrical - DIY Chatroom Home Improvement Forum
Old 10-10-2012, 02:49 PM   #1
Question on GFCI with shared neutral
A few years ago, I ran 12/3 to 2 20A outlets using a shared neutral. I'd like to change these outlets to be GFCI, but was wondering if GFCI would work on a shared neutral, or if I could only install a single one and just cap off the other line.
dmmanning is offline   Reply With Quote
Old 10-10-2012, 04:08 PM   #2
Rewards Points: 77
I dont believe GFCIs work on shared neutrals. I ahve tried it and failed.
Maybe a real electrician can chime in though, and offer a solution.
patented is offline   Reply With Quote
Old 10-10-2012, 04:16 PM   #3
Sparky
Rewards Points: 510
GFCIs will work on a shared neutral, but you have to keep line neutral and load neutral seperate
Techy is offline   Reply With Quote
Old 10-10-2012, 04:22 PM   #4
Rewards Points: 1,548
You can put ground fault circuit interrupter units on a multiwire branch circuit wherever you wish to.
But if you want to continue protection from one GFCI receptacle to additional plain receptacles, you need a separate 2 wire cable off of the load terminals of the GFCI receptacle.
Old 10-10-2012, 04:31 PM   #5
Rewards Points: 77
Actually, now I remember what I was trying to do was install a GFCI breaker on a shared neutral circuit. <---- This did not work for me.
Old 10-10-2012, 04:50 PM   #6
I've had trouble with GFCI breakers, as well - especially when the actual load is a long ways away. Not sure why... For instance, an outlet on a lamppost 100-feet from the house never worked.
Thanks for the other responses. I'll put two GFCI's at the end of the 12/3 and then run 12/2 to any other outlets beyond that.
Old 10-10-2012, 06:06 PM   #7
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Then you had a neutral to ground short, or another neutral related issue. I can assure you right now, the issue was not with the GFCI breaker.
Old 10-10-2012, 07:09 PM   #8
For very long runs beyond a ground fault circuit interrupter, induced currents (due to capacitance) between hot and ground could be sufficient to trip the GFCI.
Old 10-10-2012, 07:17 PM   #9
E2 Electrician
Not that I don't agree with you... But seriously. You want to give me the exact length that this occurs at? The reason I bring it up, is because I've never witnessed this in the field... I use a meggar and always find an insulation break down.
Old 10-10-2012, 07:48 PM   #10
Electrical Contractor
kbsparky's Avatar
I've seen it.
We did a pool installation with a rather long feeder conduit. Instead of using several GFCI breakers, we installed a big one on the feeder, protecting the entire pool panel from the source.
Nuisance tripping occurred, even with all the loads turned off.
This was a new installation, with THWN wires installed in PVC conduit.
Ended up having to scrap the idea of Ground-fault protection on the feeder, and used individual breakers on each piece of equipment.
Never had another problem after that.
-KB
Old 10-11-2012, 06:43 AM   #11
If you put the single large GFCI unit out at the pool house rather than at/in the main panel then I would not expect nuisance tripping.
Old 10-12-2012, 05:32 AM   #12
kbsparky's Avatar
There was no "pool house" -- DUH ...
Besides, you can NOT back-feed a GFCI breaker and use it as a main in a panel
-KB
Why can't you connect Ground/Neutral bus bars on a sub secutanudu Electrical 42 11-07-2012 01:33 PM
G.E. panel neutral lug question. exhdo1 Electrical 3 12-07-2011 09:33 AM
GFCI Question wildjuanpablo Electrical 7 11-28-2011 07:54 PM
Shared Neutral BobSmitt Electrical 22 09-21-2011 02:26 PM
Hot Tub GFCI Grounding Question kearnak1420 Electrical 3 04-30-2008 05:48 PM