Question About Wiring A/C To Circuit Panel? - Electrical - DIY Chatroom Home Improvement Forum
Old 08-25-2013, 05:33 PM   #1
Rewards Points: 160
Question about wiring A/C to circuit panel?
Im just trying to understand if this is correctly installed. The Volt max for my A/C is 253. My AC is connected to a 30A double pole breaker with 10-2 romex cable.
If you notice in the picture there is a hot and a neutral connected to the breaker for the A/C,is this normal?
Question about wiring A/C to circuit panel?-20130825_164802.jpg
word2yamutha is offline   Reply With Quote
Old 08-25-2013, 05:36 PM   #2
Licensed electrician
Rewards Points: 1,788
You have two hots connected to the breaker. The white should be re-identified as a hot.
Old 08-25-2013, 05:58 PM   #3
Rewards Points: 150
A 240 volt circuit uses the other phase and vice versa as a return 60 times a second. So there is no need for a neutral, just ground. White wire in panel should be marked with black electrical tape to be identified as a hot wire.
romex1220 is offline   Reply With Quote
Old 08-26-2013, 03:05 PM   #4
Rewards Points: 170
This is correct, however as a past user has stated the neutral should be re-identified. However I would not do it anymore unless you are comfortable with how the panel works and what is live since to do this you will need to remove the breaker to get tape around the wire... or risk getting dangerously close to 240v of electricity. Also I notice you have tandem breakers using 12-3 and 15-3 wire. if I am correct, since the power goes through a single cable, this is not code since you have to turn off multiple breakers to remove power from the line. hopefully someone else will come along and either verify this or tell you otherwise.
diyer111 is offline   Reply With Quote
Old 08-26-2013, 03:58 PM   #5
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
Originally Posted by diyer111 View Post
Also I notice you have tandem breakers using 12-3 and 14-3 wire. if I am correct, since the power goes through a single cable, this is not code since you have to turn off multiple breakers to remove power from the line
It's possible that the black from one cable and the red from the same cable are wired to circuits 5A & 7B and the black and red from the other cable is on 5B & 7A.
The code didn't require handle ties until I think '05?
However, if these MWBC's are on the same leg, then you run the possibility of up to 40 amps on the neutral.
Only the OP can verify this.
wirenut1110 is offline   Reply With Quote
Old 08-26-2013, 04:57 PM   #6
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,974
Looks to me like the 20A tandem has #12 on it and the 15A tandem has #14. So in this case it is very wrong. I've seen it many times with handymen and uninformed DIYers.
Shame really, that panel is pretty neat.
Old 08-26-2013, 04:58 PM   #7
Oh, and the white wire in question is NOT a neutral that needs to be re-identified. It is simply a white wire.
The Following User Says Thank You to Speedy Petey For This Useful Post:
stickboy1375 (08-26-2013)
Old 08-26-2013, 05:06 PM   #8
Semi-Pro Electro-Geek
Rewards Points: 2,970
I hadn't noticed that. It may or may not be a violation to have separate breakers on the two hots in the 3-conductor cable, depending on what's at the other end. The bigger problem is overloading the neutrals. If those are wired with the black and red from one cable on the same tandem breaker, then the neutral carries the sum of the currents instead fo the difference and is overloaded.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is offline   Reply With Quote
Old 08-26-2013, 05:12 PM   #9
E2 Electrician
stickboy1375's Avatar
Neutral is ALWAYS white, white isn't ALWAYS neutral.... not sure why people keep saying a neutral conductor is connected to a breaker, white is ONLY a color, how it is landed is a totally different story.
The Following User Says Thank You to stickboy1375 For This Useful Post:
Speedy Petey (08-26-2013)
Old 08-26-2013, 05:29 PM   #10
Rewards Points: 160
So my understanding is I have the wrong gauge of wire for the tandem breaker? I thought 12# wiring was for 20A breakers and 14# wiring was for 15A breakers? I didn't do any of this wiring, but I did add a new line into the basement for all my network equipment.
Old 08-26-2013, 05:31 PM   #11
No, the size is correct, but both hots sharing a neutral CANNOT be on a singel tandem breaker. They must be on opposite legs of the panel. A tandem breaker has both circuits sharing the same pole.
Old 08-26-2013, 05:32 PM   #12
Rewards Points: 510
You are correct on wire size however, these 4 circuits (2 each) are sharing the same neutral.
This, will, instead of the neutral carrying the imbalanced load, it will carry the sum of the 2 loads which could be 40 amps and 30 amps respectively.
Old 08-26-2013, 05:35 PM   #13
Rewards Points: 510
If you got a 20151520 quad breaker that handle tied the 20's and 15's, then you would be straight
My bad, it's a BQ215215
The Following 2 Users Say Thank You to wirenut1110 For This Useful Post:
diyer111 (08-27-2013), Speedy Petey (08-26-2013)
Old 08-27-2013, 12:09 AM   #14
Rewards Points: 160
So I have a total of 3 of these tandem breakers. They are all hooked up the same and they share 1 neutral each. Would it be easier to rewire these breakers or should I go ahead and buy this breaker BQ215215 as mentioned?
Im kind of confused on how these tandem breakers are installed. So lets say for example I had one 20A tandem breaker on one side of the panel and another 20A tandem breaker on the other side. If I shared the hot wires between these 2 tandem breakers this wouldn't cause the neutral to overload? Just trying to get an understanding of this. Thanks for the help so far guys.
Question about wiring A/C to circuit panel?-img_0820.jpg
Old 08-27-2013, 02:39 AM   #15
kbsparky's Avatar
Neutral conductors can be gray. See section 200.6
-KB
Multiple Panel Question theatretch85 Electrical 7 09-29-2016 07:15 PM
Circuit Breaker Panel Height? helpless handyman Electrical 25 02-24-2014 03:06 PM
Wiring main panel without dying Maxian Electrical 8 11-18-2012 10:11 AM
Kitchen circuit re-design - Existing is a mess darlingm Electrical 5 12-31-2011 09:45 PM
Basement wiring question kupalino Electrical 8 11-14-2009 09:25 AM