Question About Underground Wire Type - Electrical - DIY Chatroom Home Improvement Forum
Old 11-24-2009, 04:11 PM   #1
Rewards Points: 79
Question about underground wire type
My ultimate goal is to put a sub-panel in my garage. Right now I'm just trying to figure out if I can use the wire I already have to do it and save a few hundred dollars. Here is a list of what I have:
Black #6 wire marked 600v THW
White #6 marked MTW (Machine Tool Wire) THW 600v
Red #6 I think it's marked the same as the white but I can't read it clearly
Blue unmarked, it's #6 and looks identical to the white
So is any of this safe to use underground in conduit?
What about indoors? I need to run about 60' to the panel indoors. I know I can't just run individual connectors across the basement. I should be safe keeping them in conduit though, right? What's the smallest size conduit I can legally keep them in indoors?
Tmb9862 is offline   Reply With Quote
Old 11-24-2009, 04:17 PM   #2
Rewards Points: 79
Ok, the red definatly says "MTW -- Type THW"
Old 11-24-2009, 04:56 PM   #3
Where are you located ?
Is the garage attached or detached ?
I'm thinking attached since you indicate indoors, you can run conduit indoors
For a sub you need 4 wires, 2 hots, white neutral & green ground (#8 will work for green)
I used 1" conduit for my 60a sub w/#6 wire, easier to pull
Old 11-24-2009, 05:05 PM   #4
Rewards Points: 79
I am located in NY.
The garage is detached. I have about 40' between the garage and the house. The panel is on the opposite end of the house so I need to go about 60' across the basement.
Actually wiring the panel is a whole different animal. I'm not quite sure how to do that and was going to research it further. I was looking at a sub-panel in a detached garage in a new house today. It looks like they only ran two hots and a neutral, the ground goes outside to a ground rod.
Right now I'm just curious if I can use the wire I already have. I do have black #8 type TW. If I do have to run a #8 from the main to the sub panel could I just use that and wrap the ends in green electric tape?
Old 11-24-2009, 05:10 PM   #5
OK, for detached you will also need 2 ground rods at the sub panel connected with #6 min wire
Neutral must not be bonded to the panel (remove green screw) & neutrals & grounds must be on seperate bus
Conduit must run from panel to panel
3 wires is old Code
New code requires 4 wire & ground rods
Check with local code for local changes/requirements
Old 11-24-2009, 06:31 PM   #6
Electrical Contractor
jbfan's Avatar
Rewards Points: 384
Unless the wire also has a W, like thwn, it can not be used is a wet location, and underground conduit is considered a wet location.
Old 11-24-2009, 07:25 PM   #7
kbsparky's Avatar
You can use a 1" or 1" PVC conduit for this project. You will need an equipment grounding conductor, minimum #10 green or bare conductor (You can strip off the insulation of the entire length of one of your #6 pieces if you want).
You are not permitted to use green tape on conductors #6 and smaller, but I have seen this practice done many times using #8 and even #10 wires ..
-KB
Old 11-24-2009, 11:30 PM   #8
Rewards Points: 79
It's not THWN, it's THW. The black #6 is "THW". The red and white are "MTW - type THW". The #8 and #10 I have are type TW. So these should all be good to go in underground conduit as they have a W in them?
Old 11-25-2009, 06:04 PM   #9
jbfan's Avatar
Rewards Points: 384
The thw is good for 65 amps, but I can not not the ampacitiy for mtw.
The tw is 30 amps for the #10 and 40 amps for the #8.
You can not remark any of the wires you have to green, so you would have to buy a green wire.
All of these wires are good for a wet location.
Old 11-26-2009, 10:35 AM   #10
Rewards Points: 79
Thank you, that's what I needed.
A couple more things I'm not positive on.
What size ground do I need going to the main panel and what size grounds do I need going to the rods? There are two replies there saying #8 and #10.
Do I need a main lug or a main breaker panel? If I need a main breaker can I use a panel with a 100 amp main breaker so long as it's protected by the 60 on the main panel or do I need to install a 60 amp main breaker in it?
What is the proper depth for the conduit?
Finding underground electric wire for driveway lights. mitch21131 Electrical 25 09-24-2012 08:52 AM
2 Wire Thermostat question vtec69 Electrical 19 10-19-2009 05:14 PM
Thermostat Wire Question TJ_in_IL HVAC 5 10-16-2009 05:57 PM
Ground Clamps Question integlikewhoa Electrical 40 02-28-2008 09:13 PM
Wire size for distance Question fburke Electrical 4 07-28-2007 09:29 AM