Hi,
I just discovered what looks to me like a fire hazard in my main service line, but I wanted to make sure before I call an electrician.
Probably 20-30 years ago, one of the previous owners of my house added on to the kitchen by pushing a wall out about 5 feet. From the way things are wired, I'm pretty sure the meter was on the wall that was moved. So the meter was moved about 20 feet along the wall, and wire in flexible conduit was run from the original weatherhead to and from the meter, and then the wires go into the house to the main panel from the original location.
The part I'm worried about is that the splice points around where the wires go into the house are bare, uninsulated wire. Both the splice from the utility's line to the wire going to the meter, and the splice coming from the meter going into the house are like this. It kind of looks like there are remnants of insulation that have fallen off, so maybe they weren't originaly bare, but I can't tell. The two hot wires are separated by a few inches and no insulation. At one point where they are close, there is a black mark on their closest point, presumably where they touched, maybe under heavy wind?
So just to make sure I'm not misunderstanding something, it is a bad idea to have these wires uninsulated, right?
greendog is offline   Reply With Quote
Old 04-22-2011, 06:51 AM   #2
Lic Elect/Inspector/CPO
The only splice that might be bare is the neutral wire. The other splices needs to covered. This is something that should be taken care of ASAP.
The splices at the service haed should be the only splices. From the meter to the panel should not have any splices.
NJMarine is offline   Reply With Quote
Old 04-22-2011, 07:08 AM   #3
The poco cable should not be laying on the roof. None of that looks good.
Old 04-22-2011, 10:44 AM   #4
Yeah, I figured both of those things were bad.
Humorously, the only wire that isn't bare is the ground. Probably because when the meter was moved, the ground didn't have to be moved; only the two hots go to/from the meter.
I bet this has been this way for 20 years at least; ignorance was bliss, but I'm going to get an electrician out here ASAP and have this fixed. Thanks for the advice.
Old 04-22-2011, 11:07 AM   #5
CodeEnforcer
HIVOLT's Avatar
I bet you that this was done without a permit and never was inspected.
HIVOLT is offline   Reply With Quote
Old 04-22-2011, 12:36 PM   #6
nap
You talking to me?
nap's Avatar
let's hope it was never inspected. I would hate to think that it was and passed.
Old 04-22-2011, 01:17 PM   #7
CodeEnforcer
HIVOLT's Avatar
You would be surprised what I have found doing inspections. The former inspector is no more because he did not inspect.
Old 04-23-2011, 01:38 AM   #8
" Euro " electrician
frenchelectrican's Avatar
Hard to see if the photo show actually two service entrance cables but if that the case it will get tricky to get it fix right the crictail item is get the POCO service entrance side taken care of it first asap.
The safest way is have a electrician come out.
There are few regulations to deal with service entrance cable comming above the roof and that have to be inspected and I know alot of POCO have guideline and clearance on the roof section you can check with your inspector or talk to the POCO and they will tell you what it need to be done to make sure it is legit.
Merci,,
Marc
DIY Comedy--PVC for main water line? Daulton Plumbing 8 03-23-2011 10:03 AM
Service Entrance Question MeanGene Electrical 10 06-25-2010 02:46 AM
Gas Line Question jasonresno HVAC 10 01-14-2010 05:18 AM
Service Question MyFriendMo Electrical 5 01-08-2010 10:27 AM
electrical service line bmancanfly Electrical 4 07-21-2009 08:07 PM