[Q]100amp Main 100amp Sub - Electrical - DIY Chatroom Home Improvement Forum
Old 11-28-2011, 10:39 PM   #1
"So I Re-Wired It"
MisterZ's Avatar
Hello all, forgive me if this has been answered. searched around but did not find an "absolute" answer
i currently have 100 amp service w/ 100 amp main breaker panel. i have a 100 amp sub panel which is installed indoors about 20' from the main.
used 2-2-2-4 wire, isolated neutral and ground, etc. the subpanel is wired properly
my main question is, can i use a 100 amp breaker in the main panel to supply the sub??
i have read several post which say you can, and several posts which say you must use at most 60 amp double pole breaker.
please be so kind and tell me the maximum size breaker i can use in the sub panel. TIA
BTW, they are both Homeline Suare D panels, and im not adding extra equipment, just separating the existing wiring for upstairs/downstairs
MisterZ is offline   Reply With Quote
Old 11-28-2011, 10:46 PM   #2
Electrical Contractor
kbsparky's Avatar
If that 2-2-2-4 cable is aluminum, then the largest breaker you can feed it with is a 90 Amp.
You do not have to change the main breaker in the sub-panel when you feed it with a smaller breaker from the main panel.
-KB
The Following User Says Thank You to kbsparky For This Useful Post:
MisterZ (11-28-2011)
Old 11-28-2011, 10:50 PM   #3
"So I Re-Wired It"
MisterZ's Avatar
thank you for the quick response. yes the cable is aluminum.
ok, so i can get a 90amp breaker then. so you are saying this wire is not rated for 100amp?? or no matter what im only allowed 90??
Old 11-28-2011, 10:56 PM   #4
kbsparky's Avatar
Correct. 90 Amp max. Table 310.16 of the NEC, [2011 edition table 310.105(B)(16)] type XHHW insulation, 75 degree termination.
There is an exception in the Code that allows a #2 aluminum cable to be protected at 100 Amp IF it supplies the entire dwelling. Since that is not the case when installing a sub-panel, that exception does not apply here.
-KB
The Following 2 Users Say Thank You to kbsparky For This Useful Post:
HouseHelper (11-29-2011), MisterZ (11-28-2011)
Old 11-28-2011, 11:14 PM   #5
"So I Re-Wired It"
MisterZ's Avatar
Excellent!! that is the info i was looking for
thank you kbsparky. this forum is great, i look forward to helping out whenever possible
Heat for a basement with Pellt Stove on Main Floor magnum44 HVAC 1 11-20-2011 09:55 AM
Main Circuit Breaker Question vladmir1111 Electrical 2 08-20-2011 09:15 PM
main lug or main breaker kenmore Electrical 14 06-18-2011 12:13 PM
Replace main panel? And lots of other ?s Bcoleman6 Electrical 13 01-22-2008 10:40 AM
main lug vs main breaker for sub panel diyll Electrical 1 01-17-2008 09:18 PM