Pvc And Wire Size - Electrical - DIY Chatroom Home Improvement Forum
Old 09-29-2010, 04:09 PM   #1
Question
pvc and wire size
If I want a 30 amp sub panel in my garage and it is 100' from my main panel. What size wire and pvc do I need?
gunner51 is offline   Reply With Quote
Old 09-29-2010, 05:20 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 254
4 #10 thwn and 3/4 conduit and a ground rod should set you on the right path.
jbfan is online now   Reply With Quote
Old 09-29-2010, 09:11 PM   #3
since it is 100' why not use #8? Voltage Drop
Still use 3/4 PVC and 4 wires
jddavis is offline   Reply With Quote
Old 09-29-2010, 10:08 PM   #4
Pulling the full 30a 240v @ 100' = 3% voltage drop
Which is acceptable
#10 is actually rated @ 35a...per 310.16....which means you could install a 40a breaker for 35a load & lower
Can't do the 40a breaker....not allowed to upsize the breaker on #10
I think I'd go to #8 & install a 50 breaker
Old 09-29-2010, 10:16 PM   #5
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
Which is acceptable
did you miss that little footnote about #10 Dave? See the asterisk on the wire size on the left and then it refers to 240.4(D)
The Following User Says Thank You to nap For This Useful Post:
Scuba_Dave (09-29-2010)
Old 09-29-2010, 10:25 PM   #6
Ah.....that means no upsizing the breaker -Yes = not allowed
I was thinking that was wrong (upsizing on #10).....but wasn't sure if it was allowed for a sub
Old 09-29-2010, 10:50 PM   #7
nap
You talking to me?
nap's Avatar
in some situations it is allowed but with it would have to fit within one of the exceptions listed in 240.4(D). I may have overlooked it but I found nothing to allow going to the next size breaker for #10 like you would be able to with feeders in general.
Tags