Properly Wiring My New 200a Meter/panel - Electrical - DIY Chatroom Home Improvement Forum
Old 03-21-2012, 08:39 PM   #1
Properly wiring my new 200a meter/panel
My new meter/main service panel has no ground bar only a neutral bar. I have been told that since it is the main (only) panel that this is fine. Does this mean that ALL ground and neutral wires to ALL circuits AND my ground rod should be connected to this neutral bar? Just doesn't seem right to me. I know that I can get/install a ground bar kit but it would be bonded to the neutral right? kinda seems redundant. I understand electricity but this is my first panel upgrade. any GOOD advice is appreciated.
Properly wiring my new 200a meter/panel-ground-1.jpg
socalsteve72 is offline   Reply With Quote
Old 03-21-2012, 08:42 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 252
That is true for the first disconnect point, in this case your main panel.
You may have to put another ground bar just for the extra space.
The Following User Says Thank You to jbfan For This Useful Post:
plummen (03-22-2012)
Old 03-21-2012, 08:46 PM   #3
Electrician
SD515's Avatar
Rewards Points: 504
Originally Posted by jbfan View Post
You may have to but another ground bar just for the extra space.
Good point jb. Also remember, you can't double-up neutrals under one screw. You usually can with the grounds. Check the panels label for that info.
Kyle
Old 03-21-2012, 08:49 PM   #4
rrolleston's Avatar
Rewards Points: 1,012
Send a message via AIM to rrolleston Send a message via Yahoo to rrolleston
Main panel or not I prefer my neutrals and grounds on separate bars.
With Electricity there is the right way to do it and the dead way. Just because it works does not make it safe.
rrolleston is offline   Reply With Quote
Old 03-21-2012, 08:56 PM   #5
Here's the reason it seems so weird to me, what is the difference to bonding neutral & ground screws on an outlet, and doing it at the meter?
Just trying to understand...........
Old 03-21-2012, 09:14 PM   #6
rrolleston's Avatar
Ground should never carry any current.
Old 03-21-2012, 09:18 PM   #7
neutral should not carry current either, esp. when bonded to ground....?
Old 03-21-2012, 09:19 PM   #8
Sparky
Rewards Points: 510
neutral wires do carry current, back to the transformer.
Techy is offline   Reply With Quote
The Following 2 Users Say Thank You to Techy For This Useful Post:
jbfan (03-21-2012), plummen (03-22-2012)
Old 03-21-2012, 09:20 PM   #9
jbfan's Avatar
Rewards Points: 252
Neutrals do carry current!
The Following 2 Users Say Thank You to jbfan For This Useful Post:
plummen (03-22-2012), rjniles (03-21-2012)
Old 03-21-2012, 09:48 PM   #10
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
I'm sorry, I can't take it. There are certain things a homeowner can do on his own when it comes to electrical work, but replacing a main panel is not one of them.
How did you cut power to the old panel? How are you going to get it hooked back up? Is the service rated for 200 Amps? Most of the time (around here in WI) you will need a permit for the power company to make permanent connections. Around here, the only people that can pull permits for electrical are master electricians with the backing of a licensed and insured electrical contractor.
The Following User Says Thank You to k_buz For This Useful Post:
Speedy Petey (03-21-2012)
Old 03-21-2012, 09:53 PM   #11
rrolleston's Avatar
Not all areas require that and after inspection the power company will come out and connect the new service and install a meter.
Old 03-21-2012, 10:28 PM   #12
First off. I do understand the theory (ac power) and am certified in DC electrical (vehicles) and have a broad construction knowledge 20+ years. so running wiring , determining loads, proper connections ect. is actually pretty basic.
I am a homeowner that is upgrading my own service (as allowed) and DID pull proper permits and WILL pass inspection. HOWEVER I am just trying to wrap my head around the fact that current is able to go back to the transformer, on the neutral bar, while being bonded to ground. Understand?
Old 03-21-2012, 10:42 PM   #13
k_buz's Avatar
Are you installing/replacing the main grounding system?
Old 03-21-2012, 11:00 PM   #14
Electrician
SD515's Avatar
Rewards Points: 504
The neutral conductor is providing the 'return' path back to the transformer. Bonding the neutral to the 'ground' at the main does a fews things. The grounds of the branch circuits and feeders that are fed by the main now have a path back to the transformer also. This will make overcurrent devices operate if there is a ground fault. Bonding the neutral conductor to the grounding electrodes via the grounding electrode conductor(s) will help stabilize the system voltage, and help protect the system from high voltage surges, like lightning.
Kyle
Old 03-21-2012, 11:20 PM   #15
Installing all new ground system ( ground rod and cold water bond) and panel upgrade/relocation
Landscape wiring question: GFCI and Breaker Amp MikeInDetroit Electrical 0 11-02-2011 10:43 AM
Old wiring to new wiring Acworld34 Electrical 3 07-11-2011 11:00 AM
Concrobium and knob and tube wiring WillK Electrical 13 02-28-2011 01:17 PM
electric wiring in house remodel wis_remod Electrical 6 04-02-2009 03:40 PM
New Home Wiring - Seeking Expert Advice Dirtrnr Electrical 3 02-10-2009 11:33 AM