Old 12-11-2012, 01:26 PM   #1
proper way to wire a bathroom
i have a full bath to wire with lights fan and gfci receptacles and want to know the proper pathway of current.
should i bring the dedicated line to the switch then to the lights and fan then to the gfci receptacle? i thought this so if the gfci trips the lights stay on?
gwilkrrs is offline   Reply With Quote
Old 12-11-2012, 01:37 PM   #2
The lights will only go out if you wire the lights on the load side of the gfci. I usually pull two circuits for the bathroom. One 20 amp for the gfci receptacle(s) and a 15 amp circuit for the lights/fan.
teamo is offline   Reply With Quote
Old 12-11-2012, 01:46 PM   #3
ok- i dont think i have enough to pull 2 for the bathroom. i planned on just the 1 dedicated 20 is this ok?
Old 12-11-2012, 01:53 PM   #4
One 20 amp circuit is fine. Is everything going in one box or do you have a separate box for the outlet and switches?
Old 12-11-2012, 02:07 PM   #5
i have 1 breaker panel box that dumps into a subpanel that will feed this addition
Old 12-11-2012, 02:42 PM   #6
Licensed Pro
Dedicated line in to the receptacle, continue power (from line side, not load side of the gfci) to the switch. Switched power to the light and fan from the switch box.
Old 12-11-2012, 02:44 PM   #7
joed's Avatar
The cable routing is entirely dependent on your layout. The way that uses the least amount of cable is the way I would do it. Just remember current code requires neutrals at the switch box.
Do not PM with questions that can be asked in a forum. I will not respond.
Old 12-12-2012, 06:34 AM   #8
nuetrals in the box? doesnt all wire have the nuetral (white)? what am i missing?
Old 12-12-2012, 07:25 AM   #9
Lic Elect/Inspector/CPO
Yes,A neutral or away to get a neutral to the box is required.
In repsonse to gwilkrrs last post
A switch may use the white conductor as a switch leg, which mean that there would be no neutral.
NJMarine is offline   Reply With Quote
Old 12-12-2012, 08:12 AM   #10
All cables have the white wire in them but they are not always used as a neutral. The white wire is used as a hot in a switch leg, so if you run power to a light or a receptacle, and run a single cable to a switch box, the white carries the hot to the switch and the black returns the hot to the device. The new code requires a neutral in all switch boxes. I think it has to do with all of the new switches that are lighted, timers, etc. Many of these switches require a neutral to operate.
The Following User Says Thank You to teamo For This Useful Post:
jbfan (12-12-2012)
Old 12-12-2012, 04:53 PM   #11
Uh oh... so I can't wire my half wall three way using this method?
OmegaWS6 is offline   Reply With Quote
Old 12-12-2012, 04:57 PM   #12
langless28's Avatar
no you cannot anymore. for my kitchen situation too, the above picture would have been easiest as far as wire running, but i had to go a different route to get a neutral in each box.
langless28 is offline   Reply With Quote
Old 12-12-2012, 05:45 PM   #13
Interesting. I passed the rough inspection last week.
Old 12-12-2012, 06:02 PM   #14
Licensed Electrical Cont.
Speedy Petey's Avatar
Your area may not be under the 2011 NEC yet.
Old 12-12-2012, 07:13 PM   #15
Licensed Electrician
k_buz's Avatar
In just about every situation in my area, I can get by without a neutral in switch boxes.
Basically, the way the code reads, if there is basement below or attic above the switch, no neutral is required.
Location...Location...Location
Bathroom light fixture-ground wire? Abber Electrical 3 11-11-2012 09:24 PM
Bathroom Fan and no grounding wire majch Electrical 1 09-03-2012 01:55 PM
Proper awg wire size to use? Suzuki91vx800 Electrical 36 06-23-2009 05:18 PM
Choosing Proper Wire size PowerEight Electrical 15 05-22-2008 01:58 AM
Bathroom problem Imreced Electrical 6 12-09-2007 12:04 PM