Old 09-05-2012, 10:36 AM   #1
Question
Proper size of generator inlet box and breaker
Hello. I'm going to run a portable generator somewhere around the 8.5k - 10k size. I plan to use a Square D Interlock kit to back feed the panel legally and safely. What is an appropriate size of inlet box to get and what is the appropriate size of feed breaker to get for the generator sizing above?
Also, if you recommend a size and can tell me the range it would be best for (for example a generator up to 15k should I go that route) I'd appreciate it!
It seems all the inlet boxes I see are 30AMP boxes ... Do they sell larger, should I need it?
ANY AND ALL SUGGESTIONS AND RECOMMENDATIONS ARE APPRECIATED!
jpbellis is offline   Reply With Quote
Old 09-05-2012, 11:42 AM   #2
J. V.'s Avatar
They sell 50 amp inlet boxes. I am not sure if they get any larger. For a 15KW generator use a transfer switch.
Old 09-05-2012, 12:13 PM   #3
[quote=J. For a 15KW generator use a transfer switch.[/quote]
Why a transfer switch?
Old 09-05-2012, 12:19 PM   #4
J. V.'s Avatar
Because I have no other idea after 50 amp.
Old 09-05-2012, 12:24 PM   #5
I see. My original question was what is the appropriate size for an 8.5k to 10k generator? I may be completley fine with a 30AMP. Looking for thoughts around proper sizing and the correct sizing of the backfed breaker?
Old 09-05-2012, 05:44 PM   #6
Watts / Volts = Amps
10K / 240 = 41.67
30 would probably be fine, but here is a 50 amp inlet:
http://www.amazon.com/dp/B000HRWGBW/..._df_B000HRWGBW
These install right on you panel, no extra box needed:
http://www.homedepot.com/buy/relianc...-kit-pk50.html
Auger01 is offline   Reply With Quote
Old 09-05-2012, 06:05 PM   #7
Licensed Electrical Cont.
Speedy Petey's Avatar
Use whatever the largest size receptacle is on the generator you get. 20, 30 or 50.
The Following User Says Thank You to Speedy Petey For This Useful Post:
stickboy1375 (09-05-2012)
Tags
backfeed, feed, generator, interlock