Old 07-10-2013, 01:30 PM   #31
With black and red both coming in, does that mean I have 60A to pull from in that sub-panel, or only 30?
scottl31 is offline   Reply With Quote
Old 07-10-2013, 01:44 PM   #32
" Euro " electrician
frenchelectrican's Avatar
If you have 30 amp breaker then it will be only 30 amp and that it.
If you use 60 amp breaker then it will be 60 amp per leg.
On the two pole breakers they are not addtive they are only 30 each not 60 at all if the breaker marked 30 amp.
Merci,
Marc
Old 07-10-2013, 01:56 PM   #33
Merci,
Marc
if that's the case, do the black and red get connected together at the sub-panel?
Old 07-10-2013, 02:01 PM   #34
The black and red conductors will land it own lug so therefore the black conductor will land on one lug and the red on other lug that is proper way to do it and as long we are on subpanel topic just remember to keep the netural et ground seperated.
Whatever you do is never ever tie black and red together otherwise you will hit a direct short circuit unless switch loop or other speical purpose then we will deal when the time come.
Merci,
Marc
Old 07-12-2013, 11:46 AM   #35
If I do the subpanel, can I use this? It was the smallest box I could find at HD. Only thing is, I looked inside it and it appears to not have a ground bar.
Old 07-12-2013, 11:50 AM   #36
Electrical Contractor
jbfan's Avatar
Rewards Points: 254
You can use that, but will have to buy a ground bar.
Do not use the green bonding screw.
Take a pic of the inside and post it.
Old 07-12-2013, 01:47 PM   #37
Hmm.. This one looks similar for a dollar less and it says it has a ground bar. Is there any problem with the fact that the breakers are exposed instead of behind a closing door?
http://www.homedepot.com/p/t/2022531...N#.UeA_4VNfPCk
Old 07-12-2013, 01:57 PM   #38
Just a quick side question here. Is the copper in the 40-50 feet of 57-year old 10/3 I removed from this wall worth anything, or should I send it to e-waste? The wire itself seems fine, but it has no ground.
Old 07-12-2013, 04:11 PM   #39
jbfan's Avatar
Rewards Points: 254
Either panel will be fine.
Scrap Copper is going for $1 plus to almost $3 per pound.
Without stripping the wire, you are in the $1 per pound area.
Old 07-12-2013, 05:18 PM   #40
Great! If I proceed with this garage circuit, and I decide to use 12/3, is it best to split the red and black evenly among the receptacles, or to split them to the top plugs for one color and bottom for the other?
Old 07-12-2013, 05:23 PM   #41
Licensed electrician
Rewards Points: 1,278
Since you need GFI protection for the receptacles it would be easier not to split between red and black. You could alternate ABAB or AABB.
Old 07-12-2013, 11:57 PM   #42
Do I need a separate GFI receptacle for each red and black, or will one work for both?
Old 07-13-2013, 12:12 AM   #43
Rewards Points: 1,192
1 Euro = $1.31 on todays close.
bobelectric is offline   Reply With Quote
Old 07-13-2013, 12:21 AM   #44
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
You will not be able to GFI protect "split" receptacles unless you install GFI breakers which are about 8-10X the cost of a standard breaker.
Old 07-13-2013, 12:48 AM   #45
K_buzz did hit right on the spot with duex pole GFCI breakers they are not cheap at all as I mention before and they do run anywhere from 60 to 100 Euros.
The best answer is use the convential two pole breakers and have a GFCI recetpales however all the downstream part of GFCI receptales you can NOT share the netural otherwise it can trip as soon you put a load on depending how it ran.
So therefore the best answer is just run MWBC until the first GFCI's then run conventail circuits after that. the reason to prevent from false tripping.
I will post one photo what it should be for proper GFCI operation however you will need convetnail two pole breaker instead of deux single pole breakers.
Hope that help you with this set up.
Merci
Marc
Receptacle Question Pete77 Electrical 17 07-08-2013 08:44 PM
Adding GFCI receptacle outdoors Dale Gribble Electrical 2 03-21-2012 02:18 PM
Electrical power disappeared from switch to receptacle craighank Electrical 3 02-19-2012 02:06 PM
Replacing duplex receptacle with nighlight - wiring question Rabu Electrical 6 05-02-2010 08:51 PM
20A or 15A receptacle ejlog Electrical 3 02-21-2005 07:29 PM