I'm moving the service entrance for my well pump house. I have the permit and the inspector has approved my plans. I failed to ask him what the proper material is for the ground rod. The current one is steel....is that ok or do I need to get a copper (or other rod)? I'm taking no short cuts since I know how important a proper ground is.
Thanks,
Jim
Jim S. is offline   Reply With Quote
Old 02-05-2009, 11:45 AM   #2
DIYer
Galvanized or what?
Gigs is offline   Reply With Quote
Old 02-05-2009, 12:08 PM   #3
Check 250.52 (5)
Rod and pipe electrodes.
Rod and pipe electrodes shall not be less than 2.5m (8ft) in length and shall consist of the following materials.
(a) Electrodes of pipe or conduit shall not be smaller than metric designator 21 (trade size 3/4) and, where of iron or steel, shall have the outer surface galvanized or otherwise metal-coated for corrosion protection.
(b) Electrodes of rods of iron or steel shall be at least 15.87 (5/8in) in diameter. Stainless steel rods less than 16mm (5/8in) in diameter, nonferrous rods, or their equivalent shall be listed and shall not be less than 13mm (1/2in) in diameter.
Id sink a copper clad rod.
rgsgww is offline   Reply With Quote
Old 02-05-2009, 12:24 PM   #4
Electrical Contractor
Grounding electrode can be minimum 3/4" galvanized or metal coated pipe.
5/8" Stainless Steel, copper, or zinc coated rods.
All Elcetrodes can not be less than 8ft.
I'm with rgsgww, copper clad rods is the way to go.
hpp58 is offline   Reply With Quote
Old 02-05-2009, 02:06 PM   #5
Whatever they stock at your local Home Depot or supply house.
Here, everything is copper clad steel. Other places seem to use galvanized. Government projects that want to waste money may specify stainless steel.
220/221 is offline   Reply With Quote
Old 02-05-2009, 05:07 PM   #6
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,864
Thanks,
Jim
Is this a service entrance, or a well pump feed? Or is it a dedicated service for just the pump house?
Old 02-05-2009, 09:05 PM   #7
Thanks for the suggestions
I picked up a copper clad rod at the local Lowes today. Tomorrow will be the adventure of driving it in. Fortunately, no rocks in the area, just clay and sand so I don't anticipate a big problem.
Speedy, this is for a service drop (meter, breakker panel, etc) which serves a small storage shed and water well - total of 50 amps. The well is the primary use.....the other circuits are for a couple receptacles and shop lights.
Thanks again,
Jim
Old 02-05-2009, 10:12 PM   #8
Keep in mind, I don't know if your inspector will pick up on this, but the service must be rated at no less than 60A for this installation.
Old 02-05-2009, 10:18 PM   #9
Speedy,
I explained it poorly. It has a 100 amp breaker box with only 50 amps worth of breakers in it. So I should be OK.
Jim
Old 02-05-2009, 10:25 PM   #10
Yup. Then you are fine.
Grounding Method Steelhead Electrical 6 02-05-2009 12:06 PM
Proper material to raise a subfloor.... Alan Building & Construction 2 06-12-2008 07:29 AM
Anyone want to take a shot at why #6 to attach antenna ground to breaker? Piedmont Electrical 44 01-08-2008 05:11 PM
NEC Question Jafsvcs Electrical 1 06-13-2007 06:45 PM
What roofing material is right for me? Grumpy Roofing/Siding 0 07-07-2004 08:41 PM