Proper install of shared neutral
I have a sub panel in my garage. From panel I have 12/3 to an outlet powering only my fridge. One of the hots (red) is capped off at the outlet and the panel.
I am getting a kegerator to put next to the fridge and was thinking this should be on a separate circuit. My plan was to run 12/2 from the fridge outlet, using the red hot, switching out the breaker in the panel for a double breaker, and sharing the neutrals.
Is this the correct way to do it? I'm pretty sure I have to pigtail the neutrals at each outlet location and otherwise I'm good to go....
benleef is offline   Reply With Quote
Old 07-10-2013, 04:19 PM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,824
You have it right. Especially about the two-pole breaker.
Don't forget, these receptacle must be GFI protected. You can use GFI receptacles ($), or you would need to use a two-pole GFI breaker ($$$).
Speedy Petey is online now   Reply With Quote
Old 07-10-2013, 04:27 PM   #3
Rewards Points: 198
Thanks. Do they need to be GFI even though dedicated circuit behind the appliance. All my other outlets are GFI protected in the garage except for my fridge one. I've heard that refrigerators may have a tendency to cause nuisance trips on gfi outlets.
Old 07-10-2013, 04:35 PM   #4
The old exception for large appliances was removed several code cycles ago. The new one at the least will need to be GFI.
GFI's and appliances have come a long way. If a refer or freezer trips a GFI today there is a reason for it. Nuisance trips are pretty rare.
The Following User Says Thank You to Speedy Petey For This Useful Post:
mpoulton (07-11-2013)
Old 07-10-2013, 04:56 PM   #5
Rewards Points: 198
Thanks! Look like I'm going to have to spend a little money on some gfi outlets
Old 07-10-2013, 10:55 PM   #6
Rewards Points: 156
Purchase on single GFI outlet, and place it at the beginning of the "daisy chain" of outlets. This one GFI will protect all other outlets in the chain that are connected to the "load" terminals on the GFI outlet. This is a good idea too, as placing a GFI outlet behind a fridge means that if it trips, you would end up having to move the fridge to reset it.
av-geek is offline   Reply With Quote
Old 07-10-2013, 11:40 PM   #7
Electrical Contractor
jbfan's Avatar
Rewards Points: 152
Can't do that with a MWBC.
Old 08-05-2013, 11:10 AM   #8
Rewards Points: 198
So each receptacle needs its own GFI outlet correct? Essentially, nothing can be connected to the load side of the outlet because of the shared neutral?
Old 08-05-2013, 11:37 AM   #9
Licensed electrician
Rewards Points: 1,054
If wired as shown, you can use 2 GFI receptacles and it will work.
Old 08-05-2013, 11:44 AM   #10
Rewards Points: 506
benleef, I wasn't aware of the GFCI requirements for refrigerator circuits, but Speedy and jbfan know their stuff.
I would think that you're correct that both need individual GFCI receptacles, and that you shouldn't use the Load side to feed other receptacles.
Installation is the Reverse of Removal.
Old 08-05-2013, 11:50 AM   #11
Rewards Points: 506
Jim and I posted roughly same time. He knows his chit too :D
Old 08-05-2013, 12:34 PM   #12
Oso954's Avatar
Rewards Points: 444
Remember that the discussion was about a refrigerator circuit in a garage.
I believe that there is still an exception (no GFCI requirement) for a refrigerator in the kitchen of a house or apartment.
Pro's, please correct me if I am wrong on that one.
Oso954 is offline   Reply With Quote
Old 08-05-2013, 01:21 PM   #13
That exception was removed from the NEC. Now all including the garage door opener receptacle require GFI protection.
Old 08-05-2013, 01:42 PM   #14
Rewards Points: 198
Thanks for the help all.
Old 08-05-2013, 03:10 PM   #15
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
Unless you live in New Jersey.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Proper techniques to install fire blocking butterkups Carpentry 10 02-07-2013 07:37 AM
Shared Neutral Old College Try Electrical 4 06-25-2010 11:07 PM
question on the "stubbie" bonding links n175h Electrical 12 10-13-2009 05:09 PM
Main disconnect neutral wiring Daniel Holzman Electrical 5 10-04-2009 02:36 PM
Proper way to install gutter flashing? Kasfidan Roofing/Siding 3 03-17-2008 01:57 AM