-   -   Proper grounding of meter main to breaker panel (http://www.diychatroom.com/f18/proper-grounding-meter-main-breaker-panel-52534/)
tns1 09-07-2009 11:44 PM
These diagrams are such a great resource. Now if only they were numbered...
If I understand the diagram below, no ground connection is shown between the meter enclosure and the breaker panel enclosure. Shouldn't it be a 4-wire connection with a bonded ground for the enclosures?
http://www.dropshots.com/stubbie4#al...09-22/19:47:22
nap 09-07-2009 11:48 PM
no. you bond at the first disconnect, which, unless the meter is a combo meter/disco is at the main disco in the panel.
the neutral is bonded in the meter base in residential meters so it is grounded via that connection.
Jim Port 09-08-2009 07:20 AM
Not all power companies permit the grounding to take place in the meter socket.
tns1 09-08-2009 09:24 AM
OK. I was comparing the diagram with the situation where the meter enclosure has a disconnect or main breaker built-in, thinking this would be the same as far as grounding. Now I see they are handled differently due to the location of the disconnect.