Proper Calculation For Circuit Size - Electrical - DIY Chatroom Home Improvement Forum
Old 02-13-2012, 07:20 PM   #1
proper calculation for circuit size
I am about to run wire for 8kw double oven, 120/240 4 wires, 80 feet one way. instruction says 'protection circuit recommended 40A'. However, i want to double check with calculation. not sure which method to use or none at all.
method A
8000 / 240 = 33.33
then
33.33 x 1.25 = 41.66
go for 50 amp breaker???
50 amp breaker x .8 = 40 amp limit.
method B
10% over 8kw
hence
8000 x .1 = 8800
8800 / 240 = 36.67
go for 40 amp breaker???
method C, no calculation needed, variance already built in???
withoutlicense is offline   Reply With Quote
Old 02-13-2012, 07:47 PM   #2
Master Electrician
Rewards Points: 3,746
A range is NOT a continuous load. 40 amps is correct.
brric is online now   Reply With Quote
The Following User Says Thank You to brric For This Useful Post:
withoutlicense (02-13-2012)
Old 02-13-2012, 07:53 PM   #3
" Euro " electrician
frenchelectrican's Avatar
Moi aussi 2X as above not a contionous load at all.
Just wired 8-3 avce 40 amp breaker and be done with it.
Just be aware of junction box location so you will have to check the manufacter specs on location due it will varies a bit so be on safe side check it out.
Merci,
Marc
Old 02-13-2012, 08:11 PM   #4
It figures. just had a brief look at the definition of continuous load. vague description but thanks anyway.
Old 02-13-2012, 10:43 PM   #5
Rewards Points: 1,442
Note that ovens cycle on and off to maintain the desired temperature. It is highly unlikely that both ovens would have cycled on and remained on together for a period of more than 3 hours, which is the defnintion of a continuous (as opposed to intermittent) load.
AllanJ is online now   Reply With Quote
Old 02-13-2012, 10:48 PM   #6
retired elect/hvac/plumb
plummen's Avatar
Location: south east of omaha/The island of misfit contractors
Rewards Points: 2,020
Being that far of a run I might suggest upgrading the wire size to a 6/3 wg instead of an 8/3 wg ,keeping the same 40a breaker
"facts" have no relevance to this discusion
Posting from a concrete bunker under a non descript barn
plummen is offline   Reply With Quote
The Following User Says Thank You to plummen For This Useful Post:
ben's plumbing (02-13-2012)
Old 02-13-2012, 10:50 PM   #7
Rewards Points: 152
Not to hijack his thread, but if you know an appliance will run continuously like an air conditioner in south Texas, should it be considered a continuous load? My two 7.5 ton units run 18 hours per day in our 110 degree heat. They never cycle until we close the door and turn off the lights.
David
n175h is offline   Reply With Quote
Old 02-13-2012, 11:01 PM   #8
plummen's Avatar
I dont know if i would consider that a continuous load or a cry for help myself
Have you had them serviced lately to figure out why theyre running so much?
Maybe its time for a replacement/upsizing
Old 02-13-2012, 11:24 PM   #9
David
David.,
I can understand the nature of southern Texas with heat wave it is simauir to our most southen France on tempture wise it is not too far off from there.
But did the HVAC contractor did look at the unit to make sure it is sized properly if sized properly it will cycle from time to time if it was undersized may have to upgrade to twin 10 tonnes units but there is a clevation with it is you will have to check the supply to see if they can handle addtional load for the A/C units.
But I can understand some unit that can run almost contionuns they will design the circuit properly to handle that.
The last 7.5 tonne unit I have see one Trane unit it did have dual compressours so it will adjust the compressour as need to for addtional load to keep it up on hevey demand.
Merci,
Marc
Old 02-14-2012, 08:17 AM   #10
The 8 gauge copper wire will be fine for the 80' (160' round trip) run in terms of wire resistance (.64 ohms per 1000'). The voltage drop at maximum draw (34 amps) will be about 3-1/2 volts or about 1-1/2 percent of 240 volts.
When sizing the conductors for voltage drop purposes you do not multiply amperes by 1.25 for continuous loads. Then given the conductor size for amperage and, if applicable, continuous load and the conductor size for voltage drop, you choose the larger of the two.
Air conditioners are considered continuous loads. The installation instructions should give a recommended breaker rating. Sometimes there is a maximum allowable breaker rating as well.
Old 02-14-2012, 11:46 AM   #11
Retired "Double E"
MoHawk's Avatar
Here is a link for a number of electrical calculators.
http://www.electrician2.com/calculators/elcal.html
MoHawk is offline   Reply With Quote
Old 02-14-2012, 11:52 AM   #12
plummen's Avatar
Im more worried about actual heat generated in the wire over that 80' when youve got a turkey sitting in there for 8 hrs getting ready for thanksgiving/christmas dinner than I am about the voltage drop,although they both have the same basic cause resistance
And the 6/3 wg does cost that much more for peace of mind
Old 02-14-2012, 12:24 PM   #13
Retired "Double E"
MoHawk's Avatar
+1 on this post!
During my 36 years working for a large electrical utility, I've seen a number of disasters from customer wiring without proper knowledge. If your calculations are in doubt or borderline I always recommend installing the next larger wire size. When cooking a holiday dinner many ranges are operated at or near maximum amperage for many hours which can generate a lot heat in the conductors & connections.
The Following User Says Thank You to MoHawk For This Useful Post:
plummen (02-14-2012)
Old 02-14-2012, 05:18 PM   #14
For a given wire size and a given number of amperes the number of BTU or calories of heat generated per foot of wire is the same regardless of the length of the wire.
Old 02-14-2012, 05:50 PM   #15
plummen's Avatar
You dont think there would be more resistance /heat built up in that wire over 80' than there would be in a piece of 6/3 going the same distance with the same load on it?
Either way I guess its not a big deal,we're just beating another dead horse here
Tags
breaker , oven , wire sizing
What is the proper way to cut CBU around windows avtck Remodeling 2 05-22-2011 07:27 AM
Size of whole house fan needed Doug Crf General DIY Discussions 20 02-26-2011 12:29 AM
pre-hung door, 32x80 is that door size or total size? RyanD Building & Construction 3 06-28-2009 11:33 PM
Proper awg wire size to use? Suzuki91vx800 Electrical 36 06-23-2009 05:18 PM
Room size X floor tile size deck hand Flooring 4 04-08-2009 05:42 PM