Old 03-11-2008, 12:51 AM   #1
Problem with Neutral Connection
I am new here and have not had much time to look around. So I apologize if this issue has been covered before.
Problem: 120v 20amp circuit stopped working out of the blue.
Receptical: Hot to ground = 120volts
Hot to Neutral = 99volts
Ground to Neutral = 50Mohms
Question: Is this an indication that the neutral is floating or comprimised? It is my understanding that the readings should be as follows:
Hot to Ground = 120volts
Hot to Neutral = 120volts
Ground to Neutral = 0Ohms.
Any suggestions would be greatly appreciated. I am planning on opening the panel tomorrow. However, seems unlikely that there is a problem seems everything has been working for 5+ years.
Thank you in advance for suggestions or comments.
Kevin
kbrigham is offline   Reply With Quote
Old 03-11-2008, 01:46 AM   #2
" Euro " electrician
frenchelectrican's Avatar
did you test with the digtail voltmeter ??
If so you may end up reading ghost voltage and the way you descrbing i am more leaning you have bad netural connection somehwere.
a very simple test is take a table lamp just plug it in and you should see it lit up or not a very simple go / no go test.
before you start working on the connection i really strongly advise ya to turn off the breaker for that circuit [ if mapped out or marked ]
it can be bad back stabbed repectale or bad wirenut connection [ backstabbed repectales are most common for netural conntion dropped out ]
Merci, Marc
Old 03-11-2008, 02:05 AM   #3
I don't use a digital meter for this type of troubleshooting. There is no load placed on the circuit. It can be hanging by a thread and still read voltage.
Always start at the source. I had one today that was installed in 2001. The neutral connection at the bus had never been sufficiently tightened and it chose Friday to stp working.
At least 1/2 the time it is at a feed thru receptical that has been backstabbed. Use logic and trace the circuit path.
SOME of your circuit may still be working so I dentify the breaker, turn it off and check all outlets/lights. If some are working you know where it stopped.
220/221 is offline   Reply With Quote
Old 03-11-2008, 07:30 PM   #4
Thanks for the responses. Turns out the Netural wire had arc'd within the SP compromising the connection. Now, I guess the question is how did this happen.
Loose to begin with??
Brother messing with the GFCI outlet?? (His history indicates he should not mess with electricity)
However it happened I was able to reterminate and verify its operation. Thanks again for the suggestions.
Kevin
Old 03-11-2008, 08:00 PM   #5
Licensed Electrical Cont.
Speedy Petey's Avatar
More than likely.
Speedy Petey is online now   Reply With Quote
Is it possible to add a 4 way switch to this configuration? irich Electrical 55 11-25-2007 10:15 AM
Sub panel grounding sluggermike Electrical 27 11-11-2007 02:23 AM
gfci problem - 120v between ground and neutral dave0419 Electrical 1 08-18-2007 01:01 AM
Suspected open/loose service neutral mrtomwj Electrical 5 09-28-2006 09:46 AM
Splice in Neutral to Panel - OK or Not? allpraisebob Electrical 4 08-12-2006 06:54 AM