-   -   Problem with 220v Advantium (http://www.diychatroom.com/f18/problem-220v-advantium-702/)
Leer 06-11-2005 03:27 AM
Can we jumper the ground and neutral connectors in the 14-30 plugin? The advantium asks for a 3 conductor grounded wire for installation. We have a 10-2wire going to the plug. The circuit breaker box has neutral and the ground hooked together. What would be the difference or problem jumpering the ground and the neutral at the plug?
Speedy Petey 06-11-2005 11:54 PM
First off, I do not know what an Advantium is. But....
I DO know that a 14-30 receptacle MUST have a 3-wire with ground feed. Normally a 10/3NM in a home.
You CANNOT!!!!! jumper the ground and neutral at the receptacle.
I know it seems simple enough, and that the ground and neutrals are on the same bars in the main panel, but this is dangerous, against code and not smart at all. It causes the ground conductor to carry current which is not what it is designed or intended to do.
You need to replace the current 10/2 with 10/3. You have no choice.
Leer 06-12-2005 08:25 PM
ground and neutral on same bar in panel
so, It will be ok to run a new line from panel to receptacle (10/3nm) even though the neutral and ground are on the same bar in the panel?
Speedy Petey 06-12-2005 10:15 PM
Yes. Once any branch circuit leaves the main panel the grounds and neutrals MUST remain isolated.
Your 14-30 will have 4 places for wires; 2- hots, neutral & ground.