Old 02-07-2009, 03:50 PM   #16
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
If amps are given, you use the corresponding HP in table 430.248 or whatever it is. or whatever table corresponding to the type motor
wirenut1110 is offline   Reply With Quote
Old 02-07-2009, 03:53 PM   #17
Idiot Emeritus
Rewards Points: 1,492
430.6 (A) (1). The first part of this section does indeed state that table values shall be used instead of actual nameplate values, but the last part states that low speed/high torque motors may have higher nameplate amps, and nameplate shall be used.
I tend to forget that this is a DIY site, not many DIYers work with motors that are say, 705 RPM, or design D!
Rob
micromind is offline   Reply With Quote
Old 02-07-2009, 03:58 PM   #18
Rewards Points: 510
It also says that if a motor is marked with amps it assumes it corresponds with that of the table. I'm not good at assumptions, I use the nameplate. Call me wrong, it's quite ok.
Old 02-07-2009, 04:18 PM   #19
Idiot Emeritus
My take on the assumed part is for sizing disconnects and starters.
For example, if we had an air compressor labeled as 5 HP 230 volts, but the motor nameplate listed the full-load amps as 12 (A lot more common than you'd think!), using table 430.248 we would assume the motor to be actually 2 HP. A size 0 starter will control a 2 HP single phase motor, where if we used the 5 HP rating we'd need a size 2. There's a substantial cost difference between a size 0 and a size 2.
Rob
Old 02-07-2009, 05:23 PM   #20
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
NEC 430.6 (A)(1) and A(2)
I believe wirenut is refering to exception 3 of 430.6(A)(1). However this exception applies to motor operated appliances. IMO this would not apply to a well pump motor. To help differeniate this is a good article to go by.
http://www.ul.com/regulators/ode/0303.pdf
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
Old 02-07-2009, 05:34 PM   #21
I am using a submersible well pump but I am not pumping from a true well. I have a creek that runs across my property. I have tapped into it with a 15 inch pipe which runs horizontally to a 24 inch vertical pipe about twelve feet deep I am pumping from. Thus the submersible pump will be in contact with the surface water from the creek.
I should have included that in my original post.
erlindbl is offline   Reply With Quote
Old 02-08-2009, 04:01 AM   #22
I have another question about the 240V. I have been reading here, and I have seen several posts which say there is no nuetral for straight 240V. I thought I would be pulling 3 wires + a ground but it looks like I only need 2 wires + a ground. The dryer outlet had 3 + a ground which confused me.
Is the 2 + a ground correct. It would be nice to save that 270 feet of wire.
Old 02-08-2009, 06:42 AM   #23
Rewards Points: 1,192
Unless the well pump has a remote control box with a start capacitor,then you need a 3wire+ground.
bobelectric is offline   Reply With Quote
Old 02-08-2009, 02:21 PM   #24
Idiot Emeritus
You'll need 2 wires + ground from the panel to the pressure switch. Then two wires + ground from the pressure switch to the control box.
If the motor has 3 wires (Black, Yellow, Red), then you'll need 3 wires + ground from the control box to the motor. If the motor has 2 wires, then you'll need 2 wires from the control box to the motor. Most motors have a green ground wire attached.
A modern dryer plug is 3 wire + ground. It has two hots, and the neutral. The dryer motor and controls are 120 volt, the heating element is 240.
Rob
Old 02-08-2009, 09:17 PM   #25
Thanks for the reply..... That makes sense now... It is a two wire pump ...