I will run a 4th wire to the Main.
Last edited by NAIL BENDER; 12-22-2011 at 01:16 PM. Reason: Can't spill or spell.?
NAIL BENDER is offline   Reply With Quote
Old 01-13-2012, 11:04 PM   #17
remember...do not let the neutral and grounding wire touch in the sub panel....the white(neutral..grounded conducotr)...floats in the sub and does not touch it...onthe other hand .the grounding wire...is bonded to the panel...and all bare wires go to it...but all white wires..that are part of 120 voltl or 120/240 volt circuit go to the floating neutral wire...good luck
marty56 is offline   Reply With Quote
Old 01-14-2012, 08:14 AM   #18
Just call me Andrew
Rewards Points: 1,020
Slightly off-topic, but, are you running a generator indoors? Even with the door open, that is a terrible idea.
Andrew
secutanudu is offline   Reply With Quote
Old 01-18-2012, 03:25 PM   #19
Hi guys, I'm wiring a detached shop as well. My inspector told me I don't need a ground rod but if running main run in conduit (buried pvc) my ground must be insulated and same guage as my hot conductors (in my case all # 2awg). Just thought you'd like to know how we roll in the "Ridge".
supermike is offline   Reply With Quote
Old 01-22-2012, 01:33 AM   #20
Hello, Im jumping in on this thread with very similar questions. 200 amp main panel on my house. 100 amp sub panel in shop, 140' away. 1 1/2 conduit buried between the two. Wanting to run normal shop tools: air compresser, saws, welders, etc. Can someone help me with the wire sizing/load calcs? Thanking you in advance for your input.
sawhorse1000 is offline   Reply With Quote
Old 01-22-2012, 01:41 AM   #21
Licensed electrician
Rewards Points: 1,024
Your inspector is wrong. A grounding electrode system is required at an outbuilding unless it is served by a single circuit 250.32. The grounding conductor from the panel is not needed to be the same size as the hot conductors. It is sized according to 250.66.
Old 01-22-2012, 08:20 AM   #22
Just call me Andrew
Jim, he is in Canada.
Andrew
Multiple Panel Question theatretch85 Electrical 7 09-29-2016 08:15 PM
new sub panel BlueBSH Electrical 11 01-22-2012 09:28 AM
Single Phase Sub Panel from 3 Phase Power supply The Quan Electrical 1 10-30-2011 07:50 AM
Project adding 3-phase power to a tenant finish project bnharbor Electrical 5 11-11-2010 06:39 AM
Melted Service Entrance Wire in Panel theatretch85 Electrical 13 08-22-2008 11:37 AM