Power To Shed / Workshop - Electrical - DIY Chatroom Home Improvement Forum
Old 10-19-2011, 02:09 PM   #1
Rewards Points: 14
Power to Shed / Workshop
Hello,
I've seen a lot of threads about installing sub panels. My shed is about 60 feet from my main panel. I'm wondering, why can't we just run a couple 12/2 (with ground) Romex cables directly to the shed, and not use a sub panel?
Thanks in advance for advise.
thomlep is offline   Reply With Quote
Old 10-19-2011, 02:21 PM   #2
Code05's Avatar
Rewards Points: 1,104
Because of this:
II. Buildings or Other Structures Supplied by a
Feeder(s) or Branch Circuit(s)
225.30 Number of Supplies. A building or other structure
that is served by a branch circuit or feeder on the load side
of a service disconnecting means shall be supplied by only
one feeder or branch circuit unless permitted in 225.30(A)
through (E). For the purpose of this section, a multiwire
branch circuit shall be considered a single circuit.
Where a branch circuit or feeder originates in these
additional buildings or other structures, only one feeder or
branch circuit shall be permitted to supply power back to
the original building or structure, unless permitted in
225.30(A) through (E).
For the purpose of this section, a multiwire branch circuit
Code05 is offline   Reply With Quote
Old 10-19-2011, 05:01 PM   #3
Rewards Points: 150
Originally Posted by Code05
Because of this:
Sometimes I hate the way the NEC words these things! Are they referring to the Sub as one big MWBC?
Sunny B. is offline   Reply With Quote
Old 10-19-2011, 05:56 PM   #4
Rewards Points: 14
err, thanks Code05. But I'm left without more understanding. I suppose on resale it'd be best to have everything done by the regs. I can live with that.
Old 10-19-2011, 06:28 PM   #5
Electrical Contractor
kbsparky's Avatar
You can NOT run "a couple of 12/2" cables, but you CAN install a single 12/3!
That will give you the equivalent of 2 circuits, but you will need to use a double-pole breaker at the house, and a suitable disconnect at the shed.
A standard 2-pole toggle switch should suffice for your disconnecting means at the shed. I prefer to use a switch guard to minimize accidentally switching off the power:
-KB
Old 10-19-2011, 08:52 PM   #6
Rewards Points: 14
Thanks Sparky! ...but does that satisfy the stuff that code05 quoted from the regs?
Old 10-19-2011, 09:02 PM   #7
jbfan's Avatar
Rewards Points: 152
Yes, that satisfies the code.
Old 10-19-2011, 09:42 PM   #8
Code05's Avatar
The NEC is a legal document, not a novel or magazine-it is what it is.
There is no such thing as a sub-panel in the NEC. Only Panelboards.
Go to your definitions in Article 100 and look up MWBC, Branch circuit, and Feeder.
Old 09-14-2013, 02:24 PM   #9
Rewards Points: 14
power to shed project
Thanks again @kbsparky !
So, I finally got around to this power-to-shed project. I have a two-pole 20-amp breaker. I will purchase 60ft of 12/3 UF cable to run to shed. This will give me two 20 amp circuits at the shed. Am I saying this right?
Thanks!
-Tom
Old 09-14-2013, 05:47 PM   #10
Rewards Points: 3,130
I assume you mean "UF" cable? And that you'll be burying it? I'd also buy more than 60 ft.
The Following User Says Thank You to md2lgyk For This Useful Post:
thomlep (09-14-2013)
Old 09-14-2013, 08:17 PM   #11
Rewards Points: 14
yes, UF cable. The kind you can put in the ground. Shed is about 50ft from the main board.
Old 09-15-2013, 05:21 AM   #12
Philly Master's Avatar
Rewards Points: 516
Exhibit 250.46 An installation in which the isolated equipment grounding conductor is allowed to pass through the subpanel without connecting to the grounding bus to terminate at the service grounding bus.
Philadelphia Master Electrician-Generac Dealer
Philly Master is offline   Reply With Quote
The Following User Says Thank You to Philly Master For This Useful Post:
kbsparky (09-15-2013)
Old 09-15-2013, 09:36 AM   #13
Rewards Points: 14
Post
Thanks for your reply on this DIYchatroom!
Do I need a "subpanel" I have a 20-amp, two-pole breaker on the main board.
Couple questions:
1) Why would I need a "sub panel" (panelboard) at the shed?
2) why not just branch-off the 12/3 UF cable into the two circuits in the shed?
By these questions, I'm not suggesting a preference, I just want to do it right.
Thanks in advance for all your responses!
Old 09-15-2013, 11:01 AM   #14
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Couple questions:
If you are running a MWBC, then no, you do not need a sub-panel, if you run a feeder, then YES, you do need a sub-panel.
Old 09-15-2013, 11:33 AM   #15
Rewards Points: 58
You do need a disconnect. A two pole switch (for MWBC) will do the trick.
The Following User Says Thank You to J. V. For This Useful Post:
stickboy1375 (09-15-2013)
Sinking Shed willise Building & Construction 3 05-04-2011 12:34 PM
Correct way to wire a shed / workshop BOAH Electrical 10 01-05-2011 11:03 PM
Add more power to the house? (kinda long) tmtrebor Electrical 5 04-30-2010 04:19 PM
Recurring Power Oddities - Regular Schedule DamienChaos Electrical 16 10-21-2009 08:45 PM
Shed Wiring bcdal Electrical 12 03-26-2008 05:51 PM