Power Pulled 600 Ft From 200A Main To 100A Box ? Size Of Wire Recommanded?? - Electrical - DIY Chatroom Home Improvement Forum
Old 10-14-2010, 11:37 PM   #1
power pulled 600 ft from 200A main to 100A box ? size of wire recommanded??
i need to pull power 600 ft from main breaker to secondary power box > i got 200A main > secondary needs to be a 100 A . Anybody could advise on size of wire i need ??
roosterpie is offline   Reply With Quote
Old 10-15-2010, 02:23 AM   #2
Electrical Contractor
kbsparky's Avatar
What is your anticipated full load current?
-KB
Old 10-15-2010, 09:09 AM   #3
Rewards Points: 1,514
I would say you need OO gauge copper wire. If the full 100 amps were to be drawn, there will be an approximate 4% voltage drop for the 240 volt loads and, if they are reasonably balanced on both legs, a 4% to 5% voltage drop for the 120 volt loads.
Voltage drop goes down proportionately with amperes for example half the draw (50 amps) means half the drop (2%-2-1/2%)
OO copper wire: 0.77 ohms per 1000 feet one way
OOO copper wire: 0.63 ohms
Old 10-15-2010, 11:44 AM   #4
" Euro " electrician
frenchelectrican's Avatar
With that kind distance it will be little cheaper to buy in alum conductors but the size of alum conductor in that distance you will need 95mm { 3/0 AWG } however there one major quirk you will need to get a reducing pin or make a reducing pigtail connector at the breaker box location due the 100 amp breaker only can take up to 50mm { #1 AWG } so you may end up have a pretty large junction box to translated the size.
Are you in USA or Canada? the code may change a bit.
Merci.
Marc
wire size for conduit run WDR Electrical 25 08-07-2010 10:38 AM
This doesnt seem right. JoulesWinfield Electrical 27 07-26-2009 07:40 PM
Wire size and Breaker size for remodel ?? Skydmark1 Electrical 12 12-15-2007 05:00 PM
Wire size for distance Question fburke Electrical 4 07-28-2007 09:29 AM
wire size wire to 10kw furnace? lochcarron Electrical 1 04-10-2005 07:43 PM