Portable Generator Wiring - Electrical - DIY Chatroom Home Improvement Forum
Old 07-23-2012, 08:05 AM   #1
Rewards Points: 125
Portable generator wiring
Hello,
Have 200amp main panel and would like to have full panel availability, of course not all at the same time. Generator will be 8kw range. Entire home is NG.
Original plan was to install interlock kit, 30 amp double pole backfed breaker and 30 amp power box inlet.
However, reading I discover the double neutral-ground bond at both the generator and the panel is not code. Unbonding the generator is frowned upon. I have read this is only a problem with GFCI protected receptacles on the generator?
It seems this code has only been around for 5 years max? So, the majority of generators are wired according to my original plan without neutral unbonding transfer switches?
I have been unable to find a 200amp 3 pole manual transfer switch to unbond the neutral-ground.
How would I accomplish having the full panel available and still be up to code with a portable generator? As stated earlier, it would seem most all portable generators have been installed with the power box, interlock kit of some kind and backfed breaker.
Thanks for any advice you can offer.
7474 is offline   Reply With Quote
Old 07-23-2012, 09:08 AM   #2
Here it is, but its not cheap:
http://www.steadypower.com/products....3Ph%2C-200A%29
I guess you decided against the permanent-automatic setup?
Auger01 is offline   Reply With Quote
Old 07-23-2012, 09:26 AM   #3
Rewards Points: 125
With prices like those I will just go with the permanent!!!
Can't get convince myself to get the permanent when we have only had about 2 hours of power outage over the past 6 years.
Was trying to do the portable to save money. Would like to use the portable, 30 amp inlet power box, 30 amp double pole backfed breaker and Square D interlock. I see this is how things have been done for almost ever but the codes have changed. But, if I am dead the money saved does me no good.
Old 07-23-2012, 09:35 AM   #4
Some portables have instructions to remove the neutral-ground bond to make them kosher with the interlock setups. Winco is one that comes to mind:
http://www.wincogen.com/tri_fuel_generators/
Old 07-23-2012, 09:58 AM   #5
Rewards Points: 125
Thanks.
I have read both ways to unbond and not to unbond. If unbonded, it can only be used with the house?
The winco 9000 costs about $2600. For that cost, I would just spend more and have a Generac 14kw installed and power my AC along with the house, not worry about set-up.
I was looking to spend about $1,500 total with generator, inlet, cord, and double pole breaker.
I can't imagine all the people with this current set-up will be changing to a 3 pole transfer switch.
Old 07-23-2012, 08:13 PM   #6
Rewards Points: 125
Please correct my set-up if needed.
1) Unbond generator, looking at Ridgid 6800 or 8000 secondary to THD 5%
2) install 30 amp power inlet box
3) 10/3 or 8/3 romex from box to panel
4) 30 double pole breaker
5) interlock kit
Thanks again
Old 07-23-2012, 08:15 PM   #7
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,992
OK
1) LEAVE generator bonded! looking at Ridgid 6800 or 8000 secondary to THD 5%
5) interlock kit
As long as you are running a cord from the genny to the inlet box you leave the genny bonded and just use an interlock.
Old 07-23-2012, 08:38 PM   #8
Rewards Points: 125
Originally Posted by Speedy Petey View Post
OK
Appreciate the reply.
I thought that electrical code stipulated you couldn't have neutral bonds at generator and panel since I will not be using a transfer switch to switch neutrals?
Old 07-23-2012, 09:01 PM   #9
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Technically you can't, but with 99% of them wired this way and a death rate of zero, seems legit to me. lol....
Old 07-23-2012, 09:04 PM   #10
Strictly speaking, if the neutral is not switched, then you should unbond the generator. With that being said many, if not most, people dont bother to unbond thier genny.
If in the future you do decide to use the generator in a stand alone mode, then it would be important to rebond the generator.
By the way, what motor comes on the Rigid?
Old 07-23-2012, 09:09 PM   #11
Rewards Points: 125
Thanks, appreciate your reply.
I have seen you mention this on other forums. How do you have yours set-up? I think you mentioned it on another forum but I have been reading so much it has all become a blur.
Does the generator require a grounding rod?
Old 07-23-2012, 09:10 PM   #12
Rewards Points: 125
Thanks. How do you have yours set-up? Does the generator require a grounding rod.
I believe the 6800 has a Yamaha and the 8000 has a Subaru, or vice versa. One better than the other?
Old 07-23-2012, 09:12 PM   #13
E2 Electrician
I am the 99%... I have a 100amp 2pole manual transfer switch...
Old 07-23-2012, 09:14 PM   #14
E2 Electrician
You only need a ground rod if you switch the neutral in the transfer switch.
Old 07-23-2012, 09:16 PM   #15
E2 Electrician
I really do think people should start installing 3 pole transfer switches and comply with the NEC, but this has been overlooked for so long, it will take a long time to educate everyone to accept this method.
Preventing portable AC leaks Anesthesiologis Appliances 2 07-20-2012 10:21 PM
Portable Gen Set - Home Connections & Distance ArtF Electrical 1 06-15-2012 10:54 PM
Portable Dishwasher hookup MagsMom Plumbing 3 06-04-2009 10:09 PM
Portable saw Question Gettingintoit Tools 10 11-03-2008 07:45 AM
Portable air conditioners; who's got one? (No draining! Yet most say draining req'd?) Deck Appliances 1 07-16-2008 10:33 PM