Pool Wiring Question - Electrical - DIY Chatroom Home Improvement Forum
Old 06-09-2012, 12:55 AM   #1
I am running power out to a sub panel for a SWG and pump to a above ground pool. I talked to a electrician where I work and he explained how i needed to run
it. I have made a diagram how he said and was wondering if it looks like it is
right and will work safe. I plan to have it bonded but did not put it in the diagram. Not sure if just by looking at diagram that you can tell if it is right or
safe but would appreciate any input. Thanks!!
SeaDog1 is offline   Reply With Quote
Old 06-09-2012, 06:57 AM   #2
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
I would have the GFCI protection out at the sub panel, and run a bigger feeder than 20 amps....
The Following User Says Thank You to stickboy1375 For This Useful Post:
SeaDog1 (06-09-2012)
Old 06-09-2012, 07:04 AM   #3
Electrician
Rewards Points: 150
Hi Seadog1, the diagram looks fine. For code, you do need a GFCI receptacle between 10 and 20 feet of the water's edge. To give you any real feedback we'd need a lot more information. Lengths of all runs. Wire size, wire type and raceway type. Volts and amps of all loads. Depth of trench, if digging. Where the wire is being run. Is there an underwater light? Are you planning any future loads for that subpanel? Hint, Switch the GFCI breaker to the sub panel.
Glennsparky is offline   Reply With Quote
The Following User Says Thank You to Glennsparky For This Useful Post:
Old 06-09-2012, 07:07 AM   #4
Electrician
Rewards Points: 150
Stickboy is right, minimum 30 amps to any subpanel as per code.
Old 06-09-2012, 07:13 AM   #5
E2 Electrician
There is no minimum amperage size, but the disconnect rating would have to be a minimum 30 amps for a two circuit install.
225.39 (B)
Old 06-09-2012, 07:20 AM   #6
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Pools can be very tricky code wise and I highly suggest that you go over every aspect of the pool wiring and anything associated with the pool.
There are a couple things I would like to point out that you need to do in this specific situation.
1) The wiring to the pool pump motor must be in conduit. No UF cable.
2) The wiring to the pool pump motor must include an insulated ground no smaller than 12AWG.
The Following 2 Users Say Thank You to k_buz For This Useful Post:
SeaDog1 (06-09-2012), stickboy1375 (06-09-2012)
Old 06-09-2012, 08:40 AM   #7
DBW
SeaDog1, have you picked out a chlorine generator yet? The one I have operates on 120v and and requires non-switched power.
Nice ACAD drawing by the way!
DBW is offline   Reply With Quote
The Following User Says Thank You to DBW For This Useful Post:
Old 06-09-2012, 10:08 AM   #8
Glennsparky thanks for your response, If I were to put a regular 30 amp breaker in place of the 20 amp GFI and move it into the main feeder of the sub panel would that work? Also I'm using 10/4 UF wire
and its about an 80' run and will be buried 24" no conduit and using all water tight connections into the boxes. The wire out of the sub panel to the pump motor and to the SWG is a 12/3 stainless braided wire like we use on a offshore tug. The pump motor says MaxAmps 7.8-7.4/14.8 and the SWG says 220-250VAC,1A,50/60HZ if that makes sense? I have no underwater light.
Old 06-09-2012, 10:15 AM   #9
Thanks for that!! Yes I have the Hayward Aqua Rite Chlorine Generator and its set up for 220 it comes with flow switch but have read it's recommended that you tie it into pump in case it fails.
Old 06-09-2012, 10:19 AM   #10
E2 Electrician
You can't use the UF wire, sorry...
Old 06-09-2012, 11:14 AM   #11
Is it because it's not in conduit or its not code?
Old 06-09-2012, 11:19 AM   #12
E2 Electrician
Doesn't meet code.... The only place you can use NM type cable for permanently installed pools is on the interior of a One-Family dwelling... You have to use conduit.
My guess on why they require this is because they don't want the equipment grounding conductor being compromised.
Old 06-09-2012, 11:26 AM   #13
Thanks for your input! So even if I put it in conduit I still can't use that wire?
Old 06-09-2012, 11:28 AM   #14
E2 Electrician
That would be correct... You really should run a larger feeder out to that panel anyway, you need a general purpose gfci protected receptacle not less than 10' and not more than 20' from the inside wall of the pool.... ( the 10' min is from the 2005 nec, I know this changed to 6' in later editions of the NEC, so you'll have to check this one out depending on where you live)
Old 06-09-2012, 11:35 AM   #15
That would be correct... You really should run a feeder out to that panel anyway, you need a general purpose gfci protected receptacle not less than 10' and not more than 20' from the inside wall of the pool.... ( the 10' min is from the 2005 nec, I know this changed to 6' in later editions of the NEC, so you'll have to check this one out depending on where you live)
Thats why I call this @%$! pool anotherhundred every time I turn around its another $100.....what wire do I need to use?....never mind I see your Quote!
120v gas range wiring question Redfishjoe Electrical 5 05-11-2011 10:37 PM