Old 05-09-2012, 05:11 PM   #1
Pool wiring
I have only three 10AWG wires to work with which run from the house to the pool approx. 100ft. I have two main devices to connect, a pool pump (220VAC, 8A) and a pool heater (120VAC, 15A maximum) as well as a couple lights and plugs. I was going to put a double pole 30A breaker in the house to protect the 10AWG wires and then connect the two poles first to the pool pump (8A) and then to a breaker box to have the heater on a breaker from one 15A breaker on one pole and then the lights and stuff on the other.
I wanted to know if my solution is O.K. and if there are any better answers.
Thanks in advance!
chrisgill is offline   Reply With Quote
Old 05-09-2012, 05:17 PM   #2
Electrical Contractor
rrolleston's Avatar
Send a message via AIM to rrolleston Send a message via Yahoo to rrolleston
Pool wiring
You will need two hots a neutral and a ground four wires to the pool of you want to be able to use 120 240 at the pool.
Please ask me about my special discount for people that shut up and stay out of my way! With Electricity there is the right way to do it and the dead way. Just because it works does not make it safe.
rrolleston is offline   Reply With Quote
The Following User Says Thank You to rrolleston For This Useful Post:
gregzoll (05-09-2012)
Old 05-09-2012, 06:22 PM   #3
Master Electrician
Pool wiring
Thanks in advance!
Check to see if the heater can be connected at 240 volts or 120 volts. If it is dual voltage then both the heater and the pump can use the same 240 volt circuit.
brric is offline   Reply With Quote
Old 05-10-2012, 01:25 AM   #4
" Euro " electrician
frenchelectrican's Avatar
Pool wiring
What kind of 10 AWG conductor you have there ?
Is this is a UF cable or THHN in conduit ( pipe ) ??
Unforetally you will have to make a choice either stay with 120 volts or 240 volts but can not use both if you only have three conductors there and what colours as well ?
The best answer is run full 4 conductor from your panel to the pool pump panel ( Note : NO bare ground conductor is allowed on the outdoor part so you will have to run green THHN/THWN conductor this part will be well covered on pool system in NEC )
Merci,
Marc
Geothermal heat pump using pool as heat sink mnschu HVAC 9 05-17-2012 09:10 PM