Pool Sub Panel wire / conduit questions
Hello experts...
I am wiring a Pool Sub panel on the back corner of my house, the distance from my main to the exit point of the structure is 22 inches, through one framing stud.
My main is in a finished basement. I have removed the wall board between the main and the back corner of the house and have one stud to go through. Then the sub is mounted on the outside 3ft from the corner of the house. The sub panel is rated at 125v It came with a 220v 50a GFIB and I am adding two 120v GFIB in the sub. Sooooo. Here are my questions;
1. coming out of my main to the exit point of my framed wall I believe I need a 6/3 + bare AWG romex type of wire, which then splices into the 6 awg THWN (2 hot legs, 1 common, 1 ground?) and goes to the lugs, grounding and neutral bars in the Sub. It seems terrible that I have to splice the two types of wire for such a short run but I want to be in compliance and safe. Thoughts?
2. If I do have to splice the two, then where is the best place to spice- just inside of the house in a box (this could be bad as the wall would hide the access unless I modifed it) or can the spice be in a LW or other type of watertight junction box on the outside of the house. THANK YOU, DIY AL
02-02-2008, 03:33 PM
#2
Electrician
is the new panel being monted right to the house? if so then why splice? also, why even use a panel? where is the pool located? and what equipment are you wiring?
Personally, wiring a pool is not a DIY project...
02-02-2008, 03:47 PM
#3
You cannot feed a pool panel with cable.
02-02-2008, 04:00 PM
#4
Electrician
This is correct, thanks I completely overlooked the fact that he wanted to use NM....
02-02-2008, 05:02 PM
#5
Oldbie
Okay, you say no NM, then is it THWN all the way? and if so, Do I run it in conduit inside my wall for the 22" or can I just go through the stud like you can with a 12/2 or other cable? Have to use sub, as my main is nearly full. Thanks
02-02-2008, 05:09 PM
#6
Floor Sweeper
THHN / THWN has to be in conduit the whole way. You cannot run it through studs like NM.
I agree. If you attempt this, you should review NEC article 680 on pools.
02-02-2008, 05:10 PM
#7
Oldbie
Chris, the panel is mounted to the house but on a painted board that has the rest of the boxes (saltwater control, timer, low voltage transformer for pool light) Plus the panel acts as the breaker and as the visible disconnect/shutoff required by code. Pool is 21 ft away from panel a 20x40x10 deep inground. I have done everything myself, from digging the hole to mixing the cement so far. my equipment = 220 15a two speed two horse hayward pump. 220v 2.5 amp duo clear salt system, 300 watt 12v transformer powering a 12v 300 wat colorlogic led underwater pool light.
I have all my other connections complete, electrical inspection is tuesday 5 Feb. Thanks
02-02-2008, 05:22 PM
#8
Oldbie
Junkcollector, thanks, I have read 680, but it doesn't tell me how to power the sub panel, just how it has to be from the panel to the pool equipment.
So lets look at this..... On the outside of my house my conduit is 3/4' pvc LB box-2ft grey pvc coupled to 1ft liquid tight (to make the bend, (90 sweep was too big) into the sub panel.
Correct me please......PVC cannot go from the outs LB box on the outside to the main by going the 22 inches through my wall right? so do I have to use metal conduit on the inside? I saw some LB boxes that had screws in the couplings to accept metal conduit. Confused
02-02-2008, 05:45 PM
#9
Floor Sweeper
I'm confused now... All I meant is that the individual THHN wires cannot go through studs. PVC conduit can go through the wall. All LB covers need to remain accessible.
02-02-2008, 05:58 PM
#10
Eibwen
Can you mount the sub panel inside and just use switches for the service disconnects outside at the pool equiptment?
#11
Oldbie
Junkcollector, Sorry for the confusion  I see posts saying NO PVC inside of homes...The LB conduit body will be accessible as it is on the outside of the house. My problem is that I must run the THHN /THWN in conduit inside the wall, but it is my understanding that it cannot be PVC once inside the house, so I must transitions to RMT or maybe I can us ENT (the stuff some folks call "Smurf tube"
I CAN FIGURE OUT HOW TO BUILD A POOL ON MY OWN.....BUT I AM STUCK ON A 22 INCH WIRE RUN  Thanks for all your help it is greatly appriciated..
02-02-2008, 06:00 PM
#12
Oldbie
Sammy, Thought about that, but I don't think I want all that equipment in my game room (thats where my Main is located) I kinda want a "Pool control central" right where the pump, filter, valves and solar controls are
02-02-2008, 06:51 PM
#13
Oldbie
Okay, I see it now....3/4 ENT out of the main to the LB conduit body secured at the main with a ENT snap Coupling and at the LB with glue, liquid tight from the LB to the subpanel. 1 red, 1 black, 1 white 6 AWG Thhn/thwn and 1 green 8 AWG thhn/thwn run from main to sub in conduit system...Any problems with this...THanks guys
02-02-2008, 06:53 PM
#14
Eibwen
I know the feeling!
I gotta do some work on mine come early spring. Thinking about switching back to a salt system. Would love the solar collector but here in Va it warms up pretty quick.
02-02-2008, 06:59 PM
#15
Electrician
Personally, this is how I tackle any in ground swimming pool, I install the remote panel at the pool equipment, then either hardwire the equipment or install receptacles for each piece of equipment... but with the panel so close to the equipment it makes it a snap...  I live in the northeast so the pool pumps need to go inside in the winter so they all get cords, 3' is the maximum cord length...