Pool Bonding HELP!!!!!!!!! - Electrical - DIY Chatroom Home Improvement Forum
Old 08-23-2011, 09:09 AM   #1
Pool bonding HELP!!!!!!!!!
Hi All,
Please HELP!!!! trying to make sure my above ground pool is wired correctly.
I am having an issue when connecting bonding wire to pool motor GFCI breaker pops.
My set up....
Main panel has 30 amp GFCI breaker feeding a sub panel in the SHED.
From the shed I have 15 amp line going to a gfci outlet that the pool motor plugs into. The pool has a #6 copper wire attached to each metal point and then goes to a separate grounding rod . I then ran a #6 copper wire from this separate grounding rod to the motor casing. The motor has a pig tail that just plugs into the outlet.
The problem....
If motor is bonded to ground rod the Main panel GFCI breaker trips.
If I use a regular breaker the GFCI outlet does not trip.
If I remove the Bond from the motor the main panel GFCI works fine.
Shouldn't the motor be Bonded to the rest of the metal parts on the pool?
bgyako is offline   Reply With Quote
Old 08-23-2011, 09:22 AM   #2
Licensed electrician
Rewards Points: 1,616
Your post is somewhat confusing. Is the bond wire connected to the GFI?
You do not need the ground rod at the pool.
Old 08-23-2011, 09:37 AM   #3
The bond wire is attached to the motor. The motor has a screw on the case for bonding.
I thought the rod is needed for bonding pool?
Old 08-23-2011, 09:42 AM   #4
So you have a two pole 30 GFI in the panel and a 15 amp GFI for the pool?
Old 08-23-2011, 09:47 AM   #5
two pole 30 amp GFCI breaker in the main panel.
15 amp regular breaker in the sub panel that goes to GFCI outlet.
Old 08-23-2011, 09:56 AM   #6
Code05's Avatar
Rewards Points: 1,104
While Jim works on your GFCI issue, let me ask you a question.
What type of wiring method feeds the receptacle?
Code05 is offline   Reply With Quote
Old 08-23-2011, 10:57 AM   #7
Semi-Pro Electro-Geek
Rewards Points: 2,938
The motor must be bonded to the rest of the metal parts (the equipotential bonding grid). The problem you are describing sounds like the motor has a ground fault and the GFCI is doing its job. When the motor chassis is not bonded, the fault to the chassis has no path to ground so no current flows and the GFCI doesn't trip.
mpoulton is offline   Reply With Quote
Old 08-23-2011, 11:12 AM   #8
12/2 romex
Old 08-23-2011, 11:14 AM   #9
So are you saying the motor is bad?
Is the bond supposed to be isolated from the ground in the motor?
Old 08-23-2011, 11:21 AM   #10
12/2 romex
Pools require an insulated grounding conductor which neither UF or NM-B does not have. Also Type NM-B cannot be used outdoors, even in conduit.
Old 08-23-2011, 11:31 AM   #11
Code05's Avatar
Yeppers, sounds like this install was not inspected.
Old 08-23-2011, 11:32 AM   #12
Code05's Avatar
Pool bonding
Old 08-23-2011, 12:19 PM   #13
You lost me..
The bounding cable is #6 copper not insulated.
The 15 amp 12/2 romex is inside shed not outside.
It is not exposed to weather.
Old 08-23-2011, 01:08 PM   #14
Rewards Points: 1,588
How is the electricity delivered from the shed to your outlet that the pump plugs into? UF, NM, THWN, etc, underground and/or in conduit?
bob22 is online now   Reply With Quote
Old 08-23-2011, 01:18 PM   #15
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,956
I can only suggest you get a real electrician, who is familiar with pool wiring, to come out and look at this mess. There is far too much wrong here to fix via remote control.
The Following 2 Users Say Thank You to Speedy Petey For This Useful Post:
Code05 (08-23-2011), Jim Port (08-23-2011)
Bonding Pool Equipment - Conflicting Advice rickster18 Electrical 6 08-18-2011 05:21 PM
pool bonding philmymtpkts Electrical 11 08-03-2011 10:43 PM
bonding and grounding of pool pump/motor gpike19 Electrical 2 07-22-2011 12:18 PM
Tips on how I can get this electrical job done for a hot tub in backyard. the punisher Electrical 34 08-24-2010 06:08 PM
Another Pool Bonding Question RustyRealtor Electrical 4 08-05-2009 01:15 PM