I have tried to use the online wire sizing calculators and charts to determine what I am going to need and found that almost every calculator/chart gives a different answer.
120 Volts
Single Phase
Distance: 65 feet
Will be in conduit buried 18 inches
From the many calculators and charts I seem to be leaning toward these sizes and types for the following 3 loads...
1. 100 amp - #3 AWG THWN copper
2. 60 amp - #6 AWG THHN copper
3. 30 amp - #10 AWG THHN copper
Does the sizes and types look OK?
wantsomegetsome is offline   Reply With Quote
Old 05-05-2009, 11:07 PM   #2
Union Electrician
goose134's Avatar
Yes. Some may say you'll need to bump the wire size for voltage drop, but IMHO I think those sound good. Assuming you are talking copper conductors.
Now don't forget about equipment grounding conductor size, and your pipe fill.
goose134 is offline   Reply With Quote
Old 05-06-2009, 12:00 AM   #3
Rewards Points: 506
Send a message via AIM to theatretch85
Also, any wire installed in the ground or outside must be wet location rated, with single conductors in conduit this means they must be THWN rated wires. Most wire is dual rated THHN/THWN, but check to make sure it is.
theatretch85 is offline   Reply With Quote
Old 05-06-2009, 07:33 AM   #4
I meant to type THWN for all of those. I'm glad you caught that. Those where copied and pasted directly from the shopping list I'm making and it was wrong there too.
1. 100 amp = #3 THWN copper
2. 60 amp = #6 THWN copper
3. 30 amp = #10 THWN copper
4. Ground = #6 THWN copper
PVC conduit, 40% fill, two 90 degree bends = 1 inch minimum. I'll go with 1 1/2" for easier pulling.
Old 05-06-2009, 08:04 AM   #5
joed's Avatar
Rewards Points: 11,536
For a distance of 65' there is no need to upsize the wire for voltage drop. You don't need to worry about drop until you get over 150' feet with the wire.
Old 05-06-2009, 06:19 PM   #6
Bigplanz's Avatar
Rewards Points: 912
Go 2 inch in case you ever want to remove the wire and upgrade. The expense is the trench. The difference in pipe costs are negligible. Always go bigger with the pipe. Always.
Bigplanz is offline   Reply With Quote
Old 05-06-2009, 07:12 PM   #7
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,822
Where could you possibly need 30, 60 or 100 amps at 120v???
If this is for a feeder you can and should use 240v for your calculations.
I agree, 65' is not even worth thinking about VD.
Old 05-06-2009, 08:30 PM   #8
Are you saying you want to install ALL three of these circuits in your conduit, or that you are going to choose one from the list?
What is the circuit(s) for?
Willis
williswires is offline   Reply With Quote
Old 05-06-2009, 09:20 PM   #9
Smile
is wire size right for load/distance?
IMHO the wire size/load calculations are correct. But adding in the other factor; Namely, distance. Even though the presented sizes are correct. But raising the size (AWG) (this is the funny thing about AWG. The higher the # the thinner the wire. Actually, it's not humorous at all. There's a logical reason for it. The gauge is measured from the outside IN. Therefore, the closer to the core, (higher #) the thinner the wire.) will increase performance, due to Voltage Drop!!!
spark plug is offline   Reply With Quote
Old 05-06-2009, 09:31 PM   #10
[Correct] wire-size? loads/VD
You're right that 'feeder' calculations should be @ 240V. And @ 65ft., VD is not a major factor. But for individual loads the wire sizes are correct (theoretically). As far as increasing wire size; Even though Voltage drop is not a major factor @ less than 100ft+, still, it would improve performance! Again, the examples given here are mostly theoretical. With very little practical application!!!
Old 05-06-2009, 09:32 PM   #11
Originally Posted by spark plug View Post
IMHO the wire size/load calculations are correct. But adding in the other factor; Namely, distance. Even though the presented sizes are correct. But raising the size (AWG) will increase performance, due to Voltage Drop!!!
You really believe this at only 65 feet?
Old 05-06-2009, 10:31 PM   #12
From Wiki
"Increasing gauge numbers give decreasing wire diameters, which is similar to many other non-metric gauging systems. This gauge system originated in the number of drawing operations used to produce a given gauge of wire. Very fine wire (for example, 30 gauge) requires more passes through the drawing dies than does 0 gauge wire"
Old 05-07-2009, 05:56 AM   #13
The wires are to be hard wired to a deck oven. The oven has two parts, an oven and a proofer.
Oven
240 volts
12250 watts
51 amps
Proofer
120 volts
2960 watts
24.6 amps
One hot needs to be able to carry 51 + 24.6 amps = 75.6 amps
One hot needs to be able to carry 51 amps.
The neutral is only used in the 120 volt proofer part of the oven which runs at 24.6 amps.
Then the ground wire for the entire thing.
Old 05-07-2009, 06:23 AM   #14
Is this for a commercial building? If it's residential, what size service do you have?
jerryh3 is offline   Reply With Quote
Old 05-07-2009, 06:49 AM   #15
It's for my house. Main service panel is 200 amp 120/240 volt. The oven will be in operation for about 2 hours in a day about once a week. Also, the oven won't likely be running at its very maximum.
What type size mesh to keep out rats/mice? darsunt Pest Control 3 11-21-2008 11:35 AM
Nail size and Type ????? mjkpainting Carpentry 7 11-21-2008 03:06 AM
wire size for sub panel DSimo Electrical 1 07-31-2008 07:26 AM
What type / size screws for subloor project... scheenstra Building & Construction 1 05-17-2008 09:22 PM
Wire size and type in Rigid Metal Conduit Al the Diy guy Electrical 5 02-05-2008 09:31 PM